Hi-just a quick one?
I do a lot of testing but i dont often test TT systems.Am i right in saying that the earth electrode reading i get goes in the earting sytem section and not the ze box.does the ze box get n/a entered.i test using method 2 with a multifunction tester[Fluke].is there any regs stating the permitted zs for TT as the readings are high-hence earth electrode +r1+R2 as my software program always fashes up high zs when entered values
you measure your earth electrode resistence and record it in the box marked earth electrode resistance Ra,n/a for Zs.the electrode resistance should be less than 200 ohm,but anything over 100 ohm could be unstable,test should be done in least favourable conditions ie,dry.oh and keep a bucket of water handy when testing.
job ive just been on had 543 ohms on the electrode! gonna upgrade his main earth and maybe even try a new rod or summat, then **** all over the rod when testing! lol
Reply to TT system testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Recommended Sponsor News
thanks for the clarification. ( also thanks to Dan. ).