I have to disagree with you on this. The very should specifically say that the circuit does NOT comply.
It says clearly that "I certify... that the electrical installation work is in accordance with BS 7671:2008 as amended to 2015".
 
It says clearly that "I certify... that the electrical installation work is in accordance with BS 7671:2008 as amended to 2015".

"except as detailed in Part 1 above"

And in part 1 you add the details. There is the section in Part 2 "comments".


At the end of the day what should a prefessional do?

1. Issue a MWC with notes in Part 1 and Part 2

or

2. Not issue a certificate?


I would rather do 1 above!


If you are saying that ALL certificates state 100% compliance with the regs we better all give up now. Issuing a MWC with a note and comment about a potential fault is the better course of action IMHO.

Just asking for money and ignoring the issue makes us no better than bob from down the pub!
 
At the end of the day what should a prefessional do?

1. Issue a MWC with notes in Part 1 and Part 2

or

2. Not issue a certificate?

The correct answer is that you should remove the dangerous non-compliance before carrying out the work and certifying it. What you are connecting up is wholly reliant on the fault protection being present for safety, so it cannot be ignored. Likewise we are required to ensure that earthing and bonding are satisfactory before carrying out works.
 
The correct answer is that you should remove the dangerous non-compliance before carrying out the work and certifying it. What you are connecting up is wholly reliant on the fault protection being present for safety, so it cannot be ignored. Likewise we are required to ensure that earthing and bonding are satisfactory before carrying out works.

I refer you to 1 above. If the people have had a cooker connected in such away for 35 years, they may not accept your view that its not safe and needs improving.

The regs and rules are MAD IMHO.

So you would leave them without a cooker?

Then bob from the pub connects the cooker?

I will continue doing what I do....... a MWC, stating that the circuit doesn't comply is my record of flagging it to the customer...
 
Does the conection of a cooker fall within the scope of BS7671?
The fact that you would issue an MWEIC, suggests that it does.
Does either the cooker or any cables used to make the connection require ADS?
If either do require ADS, then if it is not already there, it must be provided.
 
My two pennith, would it not be the Zs that is to be considered?

Reg 411.3.2.4 TT system; each distribution circuit disconnection time not exceeding 1 sec.

Then reg 411.5.4 would give the calculation to give the maximum ZS when using a OCPD giving disconnection time of 1 sec;

Zs x Ia (less than or equal to) Uo x Cmin?
 
My two pennith, would it not be the Zs that is to be considered?

Reg 411.3.2.4 TT system; each distribution circuit disconnection time not exceeding 1 sec.

Then reg 411.5.4 would give the calculation to give the maximum ZS when using a OCPD giving disconnection time of 1 sec;

Zs x Ia (less than or equal to) Uo x Cmin?

Its a final circuit though. If disconnection is achieved by an OCPD and 411.3.1.2 is adhered to then the maximum disconnection times applicable to a TN system may be used if the circuit doesn't exceed 32A.
 
Last edited:
Its a final circuit though. If disconnection is achieved by an OCPD and 411.3.1.2 is adhered to then the maximum disconnection times applicable to a TN system may be used if the circuit doesn't exceed 32A.
Ok stand corrected.

PS but does not reg 411.5.4 apply to calculate max Zs when using ocpd on TT?
 
Last edited:

Reply to TT system with No RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
502
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
711

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top