It says clearly that "I certify... that the electrical installation work is in accordance with BS 7671:2008 as amended to 2015".I have to disagree with you on this. The very should specifically say that the circuit does NOT comply.
At the end of the day what should a prefessional do?
1. Issue a MWC with notes in Part 1 and Part 2
or
2. Not issue a certificate?
The correct answer is that you should remove the dangerous non-compliance before carrying out the work and certifying it. What you are connecting up is wholly reliant on the fault protection being present for safety, so it cannot be ignored. Likewise we are required to ensure that earthing and bonding are satisfactory before carrying out works.
An Electrical Danger Notice would be more appropriate than a Certificate though!
hum. You are going to need a very big pack if you take that approsch
My two pennith, would it not be the Zs that is to be considered?
Reg 411.3.2.4 TT system; each distribution circuit disconnection time not exceeding 1 sec.
Then reg 411.5.4 would give the calculation to give the maximum ZS when using a OCPD giving disconnection time of 1 sec;
Zs x Ia (less than or equal to) Uo x Cmin?
Ok stand corrected.Its a final circuit though. If disconnection is achieved by an OCPD and 411.3.1.2 is adhered to then the maximum disconnection times applicable to a TN system may be used if the circuit doesn't exceed 32A.