danny124

Sorry guys need help with this one,

In 12 years of being a sparks i never come had to deal with TT systems, and for the life of me can remember all the stuff i learnt back in the day and can't find any of my notes from college.


CU methods=

1. 100ma (delayed/slugged) main switch, with 30ma dual rcds with your normal mcb's

OR

2. Just a main switch but all circuits incorporating RCBO @ 30ma (can you do it this way, doubting myself and thinking it can't be done)

OSG doesn't give clear instructions and can't seem to find it in the BRB or BGB.


can someone help if possible, having one hell of a day, and having brain farts too. LOL


cheers guys
 
Time delayed Rcds are not needed much nowadays
You could use a standard twin 30 m/amp rcd board

Rcbos should ideally be double pole on a TT system
If the proposed board is metal clad,a time delay for the tails may be needed or protection of those tails on entry
 
The 30mA RCD regulations apply just the same for TT installations, as for TN installations.
100mA would be required if the tails and the CU are not both double insulated, and as a minimum for any circuits, socket-outlets, etc. that do not require 30mA RCD protection.
If using 100mA and 30mA RCDs in series, the upstream RCD will be required to be time delayed, to provide discrimination.
When setting a time delay, the requirements for TT disconection times must be allowed for. 1s for distribution circuits, and 0.2s for final circuits.
 
Sorry guys need help with this one,

In 12 years of being a sparks i never come had to deal with TT systems, and for the life of me can remember all the stuff i learnt back in the day and can't find any of my notes from college.


CU methods=

1. 100ma (delayed/slugged) main switch, with 30ma dual rcds with your normal mcb's

OR

2. Just a main switch but all circuits incorporating RCBO @ 30ma (can you do it this way, doubting myself and thinking it can't be done)

OSG doesn't give clear instructions and can't seem to find it in the BRB or BGB.


can someone help if possible, having one hell of a day, and having brain farts too. LOL


cheers guys

My preference would be the highlighted. A 100ma T/D main switch with all final circuits 30ma RCD protected by either RCBO's or a dual rcd system. Reason being as we all know RCD's fail,and with typical Ra's which will not operate an OCPD a back up RCD will prevent danger if an RCD fails to operate....the chances of two failing is IMO negligable......I believe the IEE have missed a point here,and that back up T/D RCD protection should be made a requirement on all TT systems.
That said any of the good advise by the guys will meet the current requirements.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TT System
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
danny124,
Last reply from
Deleted member 9648,
Replies
3
Views
2,154

Advert

Back
Top