just done a new ring main on a tt system ..ze at source is 355..(r1+r2)= 1.3 ..measured zs at socket 296 still more than 200ohms recommended whos responsible for getting it lower me or the provider
 
you. well, at the customer's expense, of course. TT system earthing is the customer's responsibility. bang in a couple of 5/8" screwed together rods, at least 3 ft from the building.
 
rods should be spaced 1.5 x rod length. the existing rod is probably a 3ft. twig. depth is more important. i would start afresh with screwed rods. get at least 2m depth. and away from the builder's rubble that will be next to the wall.

try to miss incoming service cables/pipes/etc. LOL.
 
rods should be spaced 1.5 x rod length. the existing rod is probably a 3ft. twig. depth is more important. i would start afresh with screwed rods. get at least 2m depth. and away from the builder's rubble that will be next to the wall.

try to miss incoming service cables/pipes/etc. LOL.

No1!! ....lol!!

As stated Depth is the key to roded TT installations, to ensure both it's stability and for enhanced Ra values... Also it's advisable to install a flush to ground concrete, or heavy duty plastic earth pit, (not one of those black PVC adaptable box things) for rod position identification and ongoing maintenance purposes...
 
No1!! ....lol!!

As stated Depth is the key to roded TT installations, to ensure both it's stability and for enhanced Ra values... Also it's advisable to install a flush to ground concrete, or heavy duty plastic earth pit, (not one of those black PVC adaptable box things) for rod position identification and ongoing maintenance purposes...
absolutely....and often overlooked....
ir they go for the `budget` option...and get one of those box cap thingys...that just perches pathetically on top of the rod.....totally unsuitable wherever theres a risk of damage to the rod.....
at the end of the day..this is the main earthing arrangements...so i cant understand why so little consideration would be paid to it....
 
absolutely....and often overlooked....
ir they go for the `budget` option...and get one of those box cap thingys...that just perches pathetically on top of the rod.....totally unsuitable wherever theres a risk of damage to the rod.....
at the end of the day..this is the main earthing arrangements...so i cant understand why so little consideration would be paid to it....

so obvious ..I've only just noticed incoming earth only 10mm will 16mm bring it down enough
 

Reply to tt system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
969
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top