just done a new ring main on a tt system ..ze at source is 355..(r1+r2)= 1.3 ..measured zs at socket 296 still more than 200ohms recommended whos responsible for getting it lower me or the provider
 
the 5/8 rods screw together and are 5ft long, 2 of them together should improve results.

all depends on your outlook mon together. side by side or screwed. like the old lady who had 2 cats that died. with being so attached to them, she decided to have them stuffed. so she went to the taxidermist to instruct him. he asked her if she would like them mounted. " no thanks" she replied. " just put them side by side"
 
The last TT install like this i did the rod was totally corroded and pulled easily out of the ground. However the Zs readings were all quite low (about 40 ohms ). It wasnt until I checked the Ze that the problem became apparent and it was parallel paths through main bonds that brought the original Zs down.

So as a thought, Scott have you also checked and confirmed theintegrity of the bonding in this property as well?
 
The last TT install like this i did the rod was totally corroded and pulled easily out of the ground. However the Zs readings were all quite low (about 40 ohms ). It wasnt until I checked the Ze that the problem became apparent and it was parallel paths through main bonds that brought the original Zs down.

So as a thought, Scott have you also checked and confirmed theintegrity of the bonding in this property as well?
you cant rely on extranious for Ze...
you need to get a stable Ra....and the only way your goin to do that is with several 5/8" rods connected together and properly sited...about a meter away from any building edges and foundation rubble.....
depth is key with TT
 
Glennspark, dont know if you misunderstood my post as I never said you could or should rely on extraneous metal to act as earth return. If i did that then why would I have bothered to checked the rod as the Zs were low anyway.

Without knowing the install i was just asking the OP if he had checked main bonds as he doesnt seem to have any parallel paths bringing down his Zs on his newly installed rfc.
 

Reply to tt system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
707

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top