the 5/8 rods screw together and are 5ft long, 2 of them together should improve results.
you cant rely on extranious for Ze...The last TT install like this i did the rod was totally corroded and pulled easily out of the ground. However the Zs readings were all quite low (about 40 ohms ). It wasnt until I checked the Ze that the problem became apparent and it was parallel paths through main bonds that brought the original Zs down.
So as a thought, Scott have you also checked and confirmed theintegrity of the bonding in this property as well?