went to house today to add a new shower circuit and as i looked at the board which was updated a year ago, i found that it is a normal spilt load board. with no 100mA rcd main switch just a normal 100A main switch with 2x 30mA rcds covering the circuit.
Now me being under impression that a tt system should have a 100mA RCD, I rang the electrician who did the work to ask why he had not installed one and he said that because all circuits in the installation are covered by the 2x 30mA rcds that a main rcd incomer was not needed.
opinions please!
he's correct. the 100mA RCD on TT went out with dual RCD boards. that's not to say you can have one fitted, bu it is now redundant.
thanks
i am just a little concerned about the 2 spare ways that are on the main switch side.
i think this time i will add a 100mA, it doesnt take much for some one to put a mcb in there thinking it'll do.
good to know for future referance though
Would be a cheaper option for future proofing to just lob the excess bus bar off
There are still uses for 100m/amp s types on a domestic TT where there is a metal clad consumer unit, if only for protection of the tails
thanks
I hear what you're saying but you can't legislate for some idiot turning up in the future and carrying out unsafe alterations/additions, where do you stop?
sounds like a better idea!
Reply to TT systems and main rcd. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...