Hi everyone.
A large industrial installation supplied with a T T System. The earth electrodes plus main earthing conductor measuring approx 10 ohms Ze. The mainswitch is a 800 amp Mccb with adjustable earth leakage.
My problem is this.
Because of the high Ze ( though not bad for TT.) the Mccb with earth leakage would ensure disconnection times at the mains position but what about say a lighting circuit at the far end of the plant.There could be two or three dis boards to get to this point and seeing as this lighting circuit would be above the max Zs do we have to install many Rcd"s with time delay,to achieve disconnection times for all circuits.

Thanks Daisy.
 
In Part 4 of the regulations the tables for max. Zs are for what sort of earthing systems? Hopefully in this installation there are further RCDs to discriminate with the main MCCB otherwise it would be very inconvenient and contrary to Regulation 314.1
 
Hi everyone.
A large industrial installation supplied with a T T System. The earth electrodes plus main earthing conductor measuring approx 10 ohms Ze. The mainswitch is a 800 amp Mccb with adjustable earth leakage.
My problem is this.
Because of the high Ze ( though not bad for TT.) the Mccb with earth leakage would ensure disconnection times at the mains position but what about say a lighting circuit at the far end of the plant.There could be two or three dis boards to get to this point and seeing as this lighting circuit would be above the max Zs do we have to install many Rcd"s with time delay,to achieve disconnection times for all circuits.

Thanks Daisy.
Hi Daisy
just a few pointers
1--your time delayed one would be closest to the origin.
2--you would have structural steelwork supplementry bonding efectively lowering
your ohmic values
3--have a look at table 41.5-----30ma Zs1553ohms
4--if each sub board is supplied TT they could be treated as "origin" ie; they could each have their
own rcd AND dedicated earth electrode,etc
 
Hi Everyone.
Thanks guys for your comments.Its confirmed to me that the installation does need more RCD"s, with discrimination.
I think TT in a large industrial installation sucks.
Thanks again Daisy.
 

Reply to TT Systems in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
609
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Replies
17
Views
529
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
I must say as well that I can only get a loop reading on the two wire hi setting, on the 3 wire low the readings are all over the place from <0.01...
Replies
5
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
834

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks