if you click on the link that ruston posted, then they list common distances that can be followed, in order to produce reliable results. thats where i got my distances from, and i remember the 60% (61.8% exactly i seem to remember) from when i was taught in the royal school of military engineering. I agree that it is a specialised field, and only substations, comms grids ect would require such accuracy.
 
if you click on the link that ruston posted, then they list common distances that can be followed, in order to produce reliable results. thats where i got my distances from, and i remember the 60% (61.8% exactly i seem to remember) from when i was taught in the royal school of military engineering. I agree that it is a specialised field, and only substations, comms grids ect would require such accuracy.

Your right 61.8% is the correct figure, but is normally rounded up to 62%. Most manufactures (including Megger), when supplying and/or selling the spike and cable earth kits will generally provide 1 X 50m , 2 or 3 X 30m cable reels. So you would be unable to follow any distances over that unless you extend using your own cable. As i said above, for single or even a twin rod system this set-up would more than suffice/

Being in the Military, you would have maybe had more cause to do quite a bit of earth rod/electrode testing in the field than most here. Did you lot, still use that insane 200 ohm maximum Ra value too?
 

Reply to TT testing. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
264
"When stoned..." Brilliant!
    • Like
Replies
6
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top