First step is to check with the supplier to see if it's available in the area (it may not be).

Edit: I guess whilst you're doing that you could be gathering R1+R2 for all the circuits to see if they'll be ok when combined with a worst case TNCS Ze (0.35).
 
Last edited:
First step is to check with the supplier to see if it's available in the area (it may not be).

Edit: I guess whilst you're doing that you could be gathering R1+R2 for all the circuits to see if they'll be ok when combined with a worst case TNCS Ze (0.35).


0.35 is by no means the worst case for PME it depends on the cutout fuse size. Ask your DNO
 
Ah, OK, ta! I was always told that 0.35 ohms was worst case you should allow for TNCS and 0.8 ohms for TNS (up to 200 ohms for TT) and if it was outside that then to contact the DNO.
 
Just found the latest figures from my local DNO for PME

main fuse size 100A max Ze 0.38 ohm
main fuse size 80A max Ze 0.52 ohm
main fuse size 60A max Ze 0.73 ohm
main fuse size 45A max Ze 1 ohm

This info was given to me a couple of months ago
 

Reply to TT to PME conversion in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
733
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top