I was careful not to state that it was generally prohibited, but the generally much higher fault currents on a reduced csa cpc and issues of adequate mechanical protection need to be considered. Really it is intended for domestic type installations and much superior choices exist for non-domestic installations. Let's be honest and agree that generally T&E is simply selected for low cost (comparatively) to proper containment systems etc.
Hi, from Amtech cable calculations, the cpc is usually less than that you would usually use in an installation. For example, if you use singles then you would use the same size cpc as the live and neutrals, but on calculations it usually can be less. Not every case but usually
 
I imagine they'll run in the cavity and not in trunking or conduit or tray, probably clipped when i think about it. Can't quite remember how i've seen this done on site. Back in the day it was conduit in the walls probably to costly for that these days. They are circuits for wall sockets. I'm actually a electrical design consultant.
Clipped in a cavity, doesn't sound right. Think the installation method needs looking at a bit more closely.
 
I was careful not to state that it was generally prohibited, but the generally much higher fault currents on a reduced csa cpc and issues of adequate mechanical protection need to be considered. Really it is intended for domestic type installations and much superior choices exist for non-domestic installations. Let's be honest and agree that generally T&E is simply selected for low cost (comparatively) to proper
I was careful not to state that it was generally prohibited, but the generally much higher fault currents on a reduced csa cpc and issues of adequate mechanical protection need to be considered. Really it is intended for domestic type installations and much superior choices exist for non-domestic installations. Let's be honest and agree that generally T&E is simply selected for low cost (comparatively) to proper containment systems etc.
I was careful not to state that it was generally prohibited, but the generally much higher fault currents on a reduced csa cpc and issues of adequate mechanical protection need to be considered. Really it is intended for domestic type installations and much superior choices exist for non-domestic installations. Let's be honest and agree that generally T&E is simply selected for low cost (comparatively) to proper containment systems etc.
You'd be surprised at the amount of commercial buildings that are wired in T&E, even when they're using trunking.
 
I was careful not to state that it was generally prohibited, but the generally much higher fault currents on a reduced csa cpc and issues of adequate mechanical protection need to be considered. Really it is intended for domestic type installations and much superior choices exist for non-domestic installations. Let's be honest and agree that generally T&E is simply selected for low cost (comparatively) to proper containment systems etc.
Surely the cable, containment and installation method you choose is dependent on the job your doing no matter if its domestic, commercial or industrial. Otherwise you just over or under engineering the job
 
Hi, from Amtech cable calculations, the cpc is usually less than that you would usually use in an installation. For example, if you use singles then you would use the same size cpc as the live and neutrals, but on calculations it usually can be less. Not every case but usually
Yes I agree that it often can be depending on fault current and disconnection time, but it remains a poor cable choice.
 
When I first started out it was a lot of over night shop fitting stuff and cut and shut office re-furbs. We used A LOT of LSF twin and earth and 3c or earth and lots of white and red FP cable to modift circuits.

Only when time and budget allowed did we put up galv conduit Or galv trunking work and wire in singles, which wasn't that often sadly
 
Why not? If T&E is suitable for the job why not use it?
As stated in my post. I am not saying dont/cant use it just expressing what I consider good design and good looking installation that is robust and easily changed, shows damage immediately, is easier to fault find on etc. Putting T&E in the fabric of the building without trunking (as the OP states) clipped (?) just seems to me poor design imho that is all I am saying. As a matter of fact I am just doing a commercial in T&E as the situation necessitates it, but not my first choice by any means. The other thing about is the whole first fix, second fix is not a big thing fitting in between framers, chippies, plasterers and plumbers etc. That whole process is a lot less complex. And don't get me started with the boarders/plasterers rather than pull the light switch wire into the hall by the door they stuffed it through the other wall in the far corner of the bedroom and other things!
 
Last edited:
When I first started out it was a lot of over night shop fitting stuff and cut and shut office re-furbs. We used A LOT of LSF twin and earth and 3c or earth and lots of white and red FP cable to modift circuits.

Only when time and budget allowed did we put up galv conduit Or galv trunking work and wire in singles, which wasn't that often sadly

OP is a design consultant and, as such, it is up to them to specify as they see fit.

While T&E might be an option, it's one that neither customer nor installer will thank them for when it comes to any future additions. I guess there are times when customers will be intransigent where price of materials are concerned, but I'd much rather see designers lead customers toward sensible solutions for their premises and not simply specify on the basis of price.

Additions can often be problematic, but it's not a great feeling when faced with a job made unnecessarily difficult at the design stage.
 
This is where the Yanks have one over on us, in commercial sites over there you aren't allowed to use soft skin cable up in the voids or under the floors. It has to be in galv flexi or galv Emt. It is not acceptable to lash in twin and earth over there, twin and earth ( romex ) is just for domestic
 
I'm pretty sure a lot of us can produce a much neater and more elegant installation with T&E
I am sure we could, funny thing is I have never seen it where T&E is concerned. Just loadsa cables thrown over suspended ceilings, lights and mixed with data cables all over the show. But then I have worked on conduit, galv and pvc looks immaculate virtually everytime. And I have looked above a lot of suspended ceilings.
 
I am sure we could, funny thing is I have never seen it where T&E is concerned. Just loadsa cables thrown over suspended ceilings, lights and mixed with data cables all over the show. But then I have worked on conduit, galv and pvc looks immaculate virtually everytime. And I have looked above a lot of suspended ceilings.
Things is usually the glav conduit installed neatly saddled up to the concrete ceiling is installed before the drop ceiling grid went up. The t&e and data wires all lashed in is thrown above the ceiling at a later date by every tom dick and harry who has worked on the site
 

Reply to twin and earth cabling size for commercial buildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for the advice! Much appreciated
Replies
6
Views
846
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top