Anybody got any thoughts on this;

I've been asked to install a new 16 amp 4 pin 415v industrial socket in a workshop to supply a lathe.....seams like an easy request, however there isnt a single distribution board in the building with a spare single phase, let alone a three phase way left on it !

There is another 32 amp 3P socket outlet in the room adjoining the area, this is used rarely, however they wish to keep it where it is for now. I've looked at the options of installing a small 4 way 3P DB next to the existing DB to supply these sockets but again no room and of course no budget for this.

Providing the protective device is suitable to protect the cable installed, i.e 32amp, would it be ok to feed the new 16 amp outlet from the same circuit by taking a SWA from the isolator above the existing outlet to the new outlet and installing a unit with a 16 amp 3 pole protective device above it to protect the outlet at 16amps as required and of course re-identifying the circuit at the DB.

There is next to no chance the two outlets will ever be used at the same time and i cant personally think of a reason why this wouldnt be ok however i've not seen it done before and theres usually a good reason for that.

Any thoughts would be much appreciated.
 
It's no different to the possibility of someone plugging 3kw heaters into every socket on a Ring main.
As long as you are protecting the cables.
 

Reply to Two 32amp outlets on one circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
801
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top