Can't find the recent thread about this, but I've been looking at smoke detectors and got this from AICO under System Installation:

"• The supply for the mains powered alarms shall be taken from an electrically protected, regularly used local lighting circuit at the nearest source except for when the house is being rewired, then the supply
will be taken back to the consumers unit and connected to the same MCB as the local lighting circuit,
confirmation of connection method shall be provided from the Contract Administrator.
• All cabling shall be as specified in Clause 411 and shall be installed in accordance with the requirements
of BS 7671:2008 3rd Amendment 2015 (17th Edition IEE Wiring Regulations) and connected in accordance
with the manufacturers recommendations. "

So, there you have it!
 
so that advice bolloxes the idea of putting them on a dedicated circuit?
 
We use Deta on new builds.
Manufacturers instructions still allow them to be on a designated circuit as long as nothing else is connected to it so the notion that they have to be installed on a local lighting circuit is rubbish
 
Hi just been on an 18th edition update seminar, and smoke alarms did come up, the man (Darren Staniforth) did comment that smokes can be on a dedicated MCB, or on which I prefer a commonly used lighting MCB, ..........so its still just as grey as it always has been
 
Hi just been on an 18th edition update seminar, and smoke alarms did come up, the man (Darren Staniforth) did comment that smokes can be on a dedicated MCB, or on which I prefer a commonly used lighting MCB, ..........so its still just as grey as it always has been

Just remember the NICEIC don’t write the rules .....

Good practice says they should be on a lighting circuit so they don’t get switched off ..... so your practice is better than his ...
 
There's clearly arguements for both, the one about having the smokes on with a lighting circuit clearly eliminates the chance of the circuit being switched off so makes a lot of sense.
If people don’t want the smokes then they will remove the head and battery if need be regardless what circuit they are on.
I’ve even seen them covered up by a shopping bag.
If they are switched off then the battery will beep anyway
 
Not actually guidance is clear in BS5839:6
... which states that (for Grade D systems):

The mains supply to the smoke alarms and heat alarms should take the form of either:
  1. an independent circuit at the premises’ main distribution board, in which case no other electrical equipment should be connected to this circuit (other than a dedicated monitoring device installed to indicate failure of the mains supply to the smoke alarms and any heat alarms); or
  2. a separately electrically protected, regularly used local lighting circuit in which case there should be a means for isolation of the smoke alarm(s) from the lighting circuit (e.g. for maintenance)
For Grade E systems, (2) is recommended.
 
I'm not really sure. But there's a note underneath the above that says:

This does not imply that there need be separate electrical protection of the smoke alarm circuit; a single means of protection against overload or short circuit (e.g. a fuse or miniature circuit breaker) serving the entire circuit is acceptable.​

Perhaps they're trying to distinguish "proper" lighting circuits from those derived from (switched) fused spurs? Not really sure, though, sorry.
 
I would say that this means that it is acceptable to run smoke detectors on the same circuit as the lighting. But not two circuits, one for smokes and one for lighting, (2 cables) lumped together in one OCPD.

There should also be a means of isolating the smokes from the lighting, ie a switch or FCU.

In fact neither 1 nor 2 in the post before the last suggest that two cables in one OCPD is acceptable.
 
There should also be a means of isolating the smokes from the lighting, ie a switch or FCU.
There is a further note (they just keep coming, don't they?!):

A number of manufacturers use a fixed base for the electrical connections, and the smoke or heat alarm can be readily removed by use of a tool operated release tab, etc.​
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Two 'Circuits' in one MCB
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Thread Tags

Advert

Thread statistics

Created
Silly Sausage,
Last reply from
happysteve,
Replies
26
Views
9,257

Advert

Back
Top