If people don’t want the smokes then they will remove the head and battery if need be regardless what circuit they are on.
I’ve even seen them covered up by a shopping bag.
If they are switched off then the battery will beep anyway
Clearly you can't account for sabotage but that's up to them isn't it
 
Not actually guidance is clear in BS5839:6
... which states that (for Grade D systems):

The mains supply to the smoke alarms and heat alarms should take the form of either:
  1. an independent circuit at the premises’ main distribution board, in which case no other electrical equipment should be connected to this circuit (other than a dedicated monitoring device installed to indicate failure of the mains supply to the smoke alarms and any heat alarms); or
  2. a separately electrically protected, regularly used local lighting circuit in which case there should be a means for isolation of the smoke alarm(s) from the lighting circuit (e.g. for maintenance)
For Grade E systems, (2) is recommended.
 
I'm not really sure. But there's a note underneath the above that says:

This does not imply that there need be separate electrical protection of the smoke alarm circuit; a single means of protection against overload or short circuit (e.g. a fuse or miniature circuit breaker) serving the entire circuit is acceptable.​

Perhaps they're trying to distinguish "proper" lighting circuits from those derived from (switched) fused spurs? Not really sure, though, sorry.
 
I would say that this means that it is acceptable to run smoke detectors on the same circuit as the lighting. But not two circuits, one for smokes and one for lighting, (2 cables) lumped together in one OCPD.

There should also be a means of isolating the smokes from the lighting, ie a switch or FCU.

In fact neither 1 nor 2 in the post before the last suggest that two cables in one OCPD is acceptable.
 
There should also be a means of isolating the smokes from the lighting, ie a switch or FCU.
There is a further note (they just keep coming, don't they?!):

A number of manufacturers use a fixed base for the electrical connections, and the smoke or heat alarm can be readily removed by use of a tool operated release tab, etc.​
 

Reply to Two 'Circuits' in one MCB in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top