Hi Guys, 4 Bed house I am going to rewire have two electricity meters. Customer want to install seprate consumer unit for upstairs on one meter and downstairs on the other one. Incoming supply is single phase with seprate cut out for each one.
my question is wheather it is allowed or not as I think there will be situation where supply from differant consumer unit will be present in switches in hallway upstairs and downstairs (staircase). Do I have to notify twice to bc? Kitchen extension and loft is new built. Any suggestion please? Thanks in advance
 
Keep upstairs and downstairs separate.
1 switch fed from upstairs C.U at the bottom of the stairs for the stairs.
And a separate switch fed from downstairs for the Hall / entrance.

It'll get confusing, as it probably already has, with Energy suppliers who won't recognise 2 meters at 1 single address.
 
They either need to get the supplier in to fit two an additional meter so it can be billed separately or fit a sub meter and the customer bills the tenant direct at an agreed price.
 
If it’s going to be two flats in the future, the customer should really be thinking about it now.
Is there two water supplies also, with no interlinking between the two? Two heating systems?
You’ll have think of fire breaks between the two properties, eg fire hoods on down lights etc.

If the customer hasn’t thought of these things now, it’ll be a huge upheaval later on
 

Reply to Two Electricity Meter in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
  • Question
This can be done. First you need a new MPAN number for the other meter. You will need to split the supply and feed SWA to upstairs coming off a...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top