Agent contacts me with an urgent request for a CU upgrade in Camden. They send over an EICR done the previous month and I have a quick skim. All seems pretty simple, CU needs an upgrade and some basic tidying of fixtures etc. Only 3 circuits so I'm not overly bothered about doing another EICR prior to doing the CU replacement.
Turn up to the property and within 10 mins I note there is no visible MET, nor is there any visible earth supply coming from the head. So I head inside and run some tests, again no earth. So I knock on the basement property and ask to test their installation, again no earth. Ok, so by this point I'm baffled by the lack of a main earth. So I called UKPN who send an engineer and he confirmed my fears, the property has never had an earth supply nor will they add one. As a result, he then issues all 4 flats with a Sec 26 ESQCR notice and turns off power to the entire building.
As you can imagine with 4 privately rented flats each with their own agents and landlords it kicks off. Turns out 2 of the 4 flats had EICRs completed within the past 3 months. One had a new CU installed. The property HAS NO EARTH!
Both EICRs were issued by NICEIC approved installers. Readings were recorded that could not have physically been taken. What is going on!?
Turn up to the property and within 10 mins I note there is no visible MET, nor is there any visible earth supply coming from the head. So I head inside and run some tests, again no earth. So I knock on the basement property and ask to test their installation, again no earth. Ok, so by this point I'm baffled by the lack of a main earth. So I called UKPN who send an engineer and he confirmed my fears, the property has never had an earth supply nor will they add one. As a result, he then issues all 4 flats with a Sec 26 ESQCR notice and turns off power to the entire building.
As you can imagine with 4 privately rented flats each with their own agents and landlords it kicks off. Turns out 2 of the 4 flats had EICRs completed within the past 3 months. One had a new CU installed. The property HAS NO EARTH!
Both EICRs were issued by NICEIC approved installers. Readings were recorded that could not have physically been taken. What is going on!?