No spare ways in the consumer unit. There are two low current radials on their own RCBOs. Do the regs forbid putting the two radials onto the same RCBO - that is two L wires into the one RCBO?
 
As a university graduate who had to extensively use and read English in studying and professionally all my life, I know simple English. I have written reams of technical documents and edited many others. It appears many cannot grasp something so fundamentally simple. Those who do not know English too well will ride along with the mob.

The text is abundantly clear - two final rings cannot be connected to one way in and CU.

Two final rings - yes I agree.

Is your argument not wandering off again though?

PS, I have a very good grasp of the English language, and have proof-read technical documents at a previous company. I don't always choose to use verbose language when typing forum posts on a mobile phone keypad however.
 
I advise you speak to people with respect, rather than repeatedly asserting that your opinion is gospel and that other people don't understand English.

If you know the answer already then why ask the question? Or was it just to create an argument?
I am being direct and open. I am not perfidious. Many here just cannot understand basic, simple English. They need to swot up. Simple.
 
Ah, you've just edited your post 74 because I pointed something out.
 
Two final rings - yes I agree.

Is your argument not wandering off again though?

PS, I have a very good grasp of the English language, and have proof-read technical documents at a previous company. I don't always choose to use verbose language when typing forum posts on a mobile phone keypad however.
Circuit not ring. It says so in the text.

The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

Point out what you do not understand.
 
Circuit not ring. It says so in the text.

The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

Point out what you do not understand.

You edited your post. Look at where I quoted you - you can't edit that to cover up your mistake.
 
The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

Point out what you do not understand.

You know full well which of your posts I was replying to. I even quoted it. You are doing your usual ducking and diving to turn things back on people.

I'm out - it's too much hard work trying to converse with you. I should have learnt my lesson after the other threads.
 
The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

Point out what you do not understand.

The regs are an imperfect painting-by-numbers scheme that if followed ought to result in an installation that complies with the statutory requirements of other legislation. They aren't statutory in and of themselves though. Not following one is not always breaking the law.

I would happily stand up in court and defend two typical lighting circuits in an RCBO as being electrically safe, especially given the considerably lower loadings of many LED infested lighting circuits these days, usually considerably lower than the original design anticipated.

I'd never stand up in court and defend a boiler radial in with a sub main as we're mixing final and distribution, wrong OCPD for boiler, and wildly different functions which could lead to incorrect isolation attempts.

The 2nd sentence in that reg says "The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated"

I can understand anyone saying this is black/white and choosing not to do it.
I can also understand anyone saying "the spirit of that reg is grouping functions together for clarity and safe isolation".
If you can summarise a circuit easily e.g. "Lighting 1st/2nd Floor" and the loading is suitable there is no reason why they can't be combined. Where they are combined is really not worth this degree of argument/upset.
 
As a university graduate who had to extensively use and read English in studying and professionally all my life, I know simple English. I have written reams of technical documents and edited many others. It appears many cannot grasp something so fundamentally simple. Those who do not know English too well will ride along with the mob.

The text is abundantly clear - two final circuits cannot be connected to one way in and CU.
As another university graduate, with a smattering of law amongst the technical stuff, who had to extensively use and read English in studying and professionally all my life, I also know simple English, and you are misinterpreting this.
 
My final input to this is a repeat of what I said earlier…

“An unfused spur may be connected to the origin of the circuit in the distribution board”

Straight out the book. Plain English.
So if we had 10 circuits with unfused spurs only, they can all go back to one way.

The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

Point out what you do not understand.
 
Status
Not open for further replies.

Reply to two radials into an RCBO in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top