daveb
-
hi folks,
Been asked to go look at a job tomorrow as his RCD is not resetting - customer sent me some details and from what I can determine is this....
It’s only socket circuits that are on the RCD side of the board. The downstairs socket circuit and the kitchen socket circuit are both off - all other socket circuits on the RCD side are on.
When he tries to flick either one of these circuits it trips the RCD? He’s unplugged everything he says, but still wouldn’t make sense as to why both circuits would all of a sudden not allow a reset?
It’s in the country so am wondering if it’s rodent damage or something on both circuit cables?