K

KNIPEX

Hi all.

im working in a small little building which has toilets/meeting rms/office kitchen etc, the water main comes in at the kitchen, ive pulled a cable in to bond this

however while in the toilets today i noticed another water main coming into the same building so it has 2, however i do not have a bond to this as ive only know just seen it.

this is a new one on me 2 water mains in the same small building, everything is cross bonded at the boilor now and if i cross bond in the toilets aswell will this be acceptable as the other water bond would therfore be cross bonded.

thanks in advance for your help.
 
It's an incomming service, it's an extraneous-conductive-part, it will be introducing earth potential - It HAS to be bonded back to the MET.
Can't believe some of the posts I've read in reply to this:confused:
 
Just as its a rising main, feeding one house, then back off to feed another? One bonding for the whole street? I stll say it needs bonding!!:)

Steve.

Sorry, what i meant was if the water stop taps were rising in the same building, i would have thought that as long as one of the taps in the same house was bonded, then that would be sufficient?
 
thanks for the replies guys, bad news is yes it has to be bonded, i spoke to the nic today and they confirmed my worst nightmare, i now have seioous issues in getting the bond to it.
 
Sorry, what i meant was if the water stop taps were rising in the same building, i would have thought that as long as one of the taps in the same house was bonded, then that would be sufficient?

Yep, that would be right Jason!! Unless, of course, the same building was divided into seperate flats etc, then each would need bonding.

Steve.
 
hi i did a job were there was no water meter or stop tap apart from the one in the street 12 meters away.every thing was cross bonded but no main bond to the water.the inspector says it is passabelhow ever you must log it in your test sheets.
what do you think?
 

Reply to Two water mains/ two bonds?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
415
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
505

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top