I understand why the increased use of type a rcds are recommended however there’s something I don’t understand. If these type a rcds aren’t tripping at 1x on a normal 50hz ac cycle or at x5 then surely they can’t be fit for purpose because they are not detecting a potentially critical fault. In my understanding an MFT simulates a fault at a specific leakage current in order to trip the rcd. Type ac rcds trip without failure most of the time. But carry out exactly the same test under the same conditions on a type a RCD it fails to interrupt the supply. Obviously there’s a type a test on the mft but why is it acceptable that they fail the ac test when the circumstances and requirement for them to trip under fault conditions on an ac circuit hasn’t changed?
 
There was and is a requirement to disconnect all live conductors for a circuit protected by an RCD

And now they have rigged the rejigged the regs to allow single pole RCBOs
Can you point me to it. Are we talking rcd or a circuit protective device such as an rcbo.
 
I am talking about RCDs but in doing so that also includes RCBOs and other such devices
I am talking rcbo, there is no requirement for them to disconnect the neutral on a TT system where their function is only circuit protection.
 
Manufacturers specify a maximum earthing resistance for their RCBO's, this may not always be met with TT systems.

For example schneider specify a max earthing resistance of 100 ohms.

Hager used to stipulate no sp RCBOs for tt systems and now it’s all ok..
Why?
Because it suits what they are selling
 
Hager used to stipulate no sp RCBOs for tt systems and now it’s all ok..
Why?
Because it suits what they are selling

Or maybe they have changed the design of their RCBO's to be suitable for use on a TT system.

I don't fit Hager so I don't know, do they have functional earth's for their RCBO's or are they the type without?
 
If we need double pole protection in TT installations, then fuses can’t be used.
So we have to condemn all those BS 3036 and BS1361 fuse boxes.
What about the DNO fuse, or plug top fuses?

Wait, what about single pole light switches?
 

Reply to Type A RCDs Vs Type AC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top