It would make sense and is in fact done in some countries the closest being the Republic of Ireland where it is referred to as neutralising.
 
If this Hot Tub is being positioned on bare ground/grass or concrete/slabs etc then you will also need to drive in a supplementary earth rod if your supply is PME/TNC-S!! Check your BGB!! lol!!!

Personally i've never come across a hot tub with such a low KW rating, i'd be installing a 6mm 3 core SWA as a matter of course for this installation.

This is why I asked what the earthing was.
 
Can you expand on this a bit please? I am doing a hot tub supply and garage supply install next week and thus far am planning to set up a seperate TT earth for the supplies as my instincts are telling me to ditch the PME for a hot tub.

Edit:

Insomnia is still bugging me so i've just read up on this in the BGB and guidance notes, references to this aren't all that obvious or big but ive found it. If i've read it right the requirement is for the addition of an earth electrode connected to the MET with a recommended Ra for the electrode of 20ohms.

I assume this prevents a dangerous potential rise in relation to true earth if a broken neutral occurs on the DNO network, and will result in a significant current flow through the rod as neutral currents are diverted. Is this in effect a bond to the local ground?

If my above assumption is correct would it not then be sensible to have this earth electrode installed for all PME supplies?



That's right, the earth rod is additional or supplementary, rather than to replace the PME earth. As you say, it would indeed be sensible to have a localised earth electrode for all PME/TNC-S supplies. Not with a value of anywhere near 100/200 ohm Ra though lol!!. This is actually a requirement in many European countries where PME supplies are provided. In effect it's another point of the protective multiple earthing system, but using the MET for the N-E connection. I'm not so sure that the additional rod would be best connected to the MET, in this case, ...i'd connect direct to the Hot Tub's main earthing terminal.... Does the hot tub have any integral RCD protection??

As for the recommended 20 Ohm Ra, like any earth electrode system, always try and get as low a value as you can, rather than just aiming for the arbitrary max value..
 
I'm not quite following the logic of bot connecting it to the MET here, would connecting it directly to the hot-tub not cause a diverted current to flow through the hot tub's CPC to the earth electrode? Especially if the dreaded lost Neutral fault was to occur on the PME supply? Bearing in mind the Ib for this hot tub is only 25A so the cable an't going to be very big.
 
If the rod is 'additional' to the PME earthing would it then not just be an extraneous-conductive-part and require main bonding to the MET.

In effect bonding the ground.
 
If you were to rod the hot tub's panel then it would have to be either isolated from the supply earth by not connecting the cable's earth at the hot tub end (creating its own TT), or you'd run a 10mm bonding cable back to the supply MET.
 
I'm thinking more towards this tub being located/positioned on bare ground or grass. I'm not really that bothered about broken neutrals on a TNC-S/PME supply, as the chance of ever seeing that, is going to be remote to say the least!! As stated i'd be installing a 3 core 6mm SWA supply cable out to this hot tub, which would provide an ample CSA of copper CPC going back to the MET. I'd probably also use a 6mm earthing conductor from the hot tubs local earth rod too!!

Bare feet on wet earth and grass, or on wet concrete is another matter altogether though, ...now you're in the realms of potential differences and step voltages!!
 
If you were to rod the hot tub's panel then it would have to be either isolated from the supply earth by not connecting the cable's earth at the hot tub end (creating its own TT), or you'd run a 10mm bonding cable back to the supply MET.

I'd be happy to have either, (if the TT was of a low value). In this case, I reckon 6 mm of copper, will do an adequate job of protection, even if it's not exactly what the BGB say's!! lol!!
 

Reply to Type C Mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
793
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
979

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top