It would make sense and is in fact done in some countries the closest being the Republic of Ireland where it is referred to as neutralising.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Type C Mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
If this Hot Tub is being positioned on bare ground/grass or concrete/slabs etc then you will also need to drive in a supplementary earth rod if your supply is PME/TNC-S!! Check your BGB!! lol!!!
Personally i've never come across a hot tub with such a low KW rating, i'd be installing a 6mm 3 core SWA as a matter of course for this installation.
Can you expand on this a bit please? I am doing a hot tub supply and garage supply install next week and thus far am planning to set up a seperate TT earth for the supplies as my instincts are telling me to ditch the PME for a hot tub.
Edit:
Insomnia is still bugging me so i've just read up on this in the BGB and guidance notes, references to this aren't all that obvious or big but ive found it. If i've read it right the requirement is for the addition of an earth electrode connected to the MET with a recommended Ra for the electrode of 20ohms.
I assume this prevents a dangerous potential rise in relation to true earth if a broken neutral occurs on the DNO network, and will result in a significant current flow through the rod as neutral currents are diverted. Is this in effect a bond to the local ground?
If my above assumption is correct would it not then be sensible to have this earth electrode installed for all PME supplies?
If you were to rod the hot tub's panel then it would have to be either isolated from the supply earth by not connecting the cable's earth at the hot tub end (creating its own TT), or you'd run a 10mm bonding cable back to the supply MET.
I'd be happy to have either, (if the TT was of a low value). In this case, I reckon 6 mm of copper, will do an adequate job of protection, even if it's not exactly what the BGB say's!! lol!!
I agree Eng. Just quoting regs really for the op
Reply to Type C Mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net