Dear all,
I have to protect a 13 amp ring main which is currently protected by a type b rcbo.The circuit is going to be used by step down transformers from the US.Notorious for tripping on start up.I thought a change to a type D rcbo would cure this,however neither MEM or Crabtree make a type D RCBO.This makes me think that perhaps im not allowed to do this.
Anyone any experience of this?
Care to explain more about the VD aspect DW ?
As I understood it modern RCD/RCBO being current operated, even if the VD falls momentarily to below 50V you would still have a massive current flow through one of the (L) main coils (on a SP RCD) to earth causing the trip coil to operate.
I am just having a think on 3 and 4 pole versions now.
I am not saying you are wrong btw, just interested in this aspect.
Edit: Having thought about the 3 and 4 pole versions, although you may indeed get a high VD, this correspondingly high current flow would not be returning via either another phase/s or the N through the magnetic core thus causing again a massive magnetic imbalance. hmm.
Ps. I don't really want to get into the high Zs/ poor design debate.
The point I was making was nothing to do with Ra values,which is another matter entirely. The point was simply that the gist of this thread is using an RCD to meet disconnection times on a TN system is always ,regardless of circumstances, unacceptable.....and yet most of the posters would have no problem with using an RCD to meet disconnection times on a TT.
Doesn't make sense.
There isn't much choice in the matter having to use an RCD to meet disconnection times in TT systems, especially UK TT systems!! .... Doesn't make the RCD device's any more reliable though!!
but you can still get as low as possible....where you know that there isn`t going to be wild fluctuations due to soil condition changes by getting under that layer...
and this means depth..
depth is key...with TT
At Sparks 68
There are many aspects of rcbo operation and theory that go very deep ...
I can explain most of them from working voltages to earth leakage masking caused by harmonics but im so tired ill only get head mush ... most operating safety devices come with a working voltage range if your voltage is out of this range then the device won't be guaranteed to function correctly sometimes its for other reasons non related to fault conditions like alot of rcd's have a minimum voltage specified due to the testing function relying on a resistor but bare with me ill get back to you on this when i can keep my eyes open.
Ill remind you my post no' 30 explains this and why RCD's on a TT are reliable due to limited volts drop but on a TN system the much higher current can render the RCD useless due to VD in fault condition hence the O/L nature of the device must then trip within the time limit - this can only be achieved if the Zs is met.
A TT system requires a different plane of thought and should not be a comparison.
That is your interpretation. But I'm an electrician,I work to Bs 7671.That is what I was taught in my apprenticeship,and if it ever goes ---- up that is what will be waved in my face in court. And Bs 7671 permits the use of an RCD for fault protection on a TN system.
Interesting debate, even made and old thicky like me think about things -- and get an appreciation of a few points I didnt understand so well as I thought! Guess it all boils down to if things go wrong and someone is gunning for your blood how you justify yourself in a court of law for your work.
BS7671 is guidance and meeting its requirements "are regarded by the HSE as likely to achieve conformity with the relevant parts of the EAWR's" but dont guarantee immunity. But not meeting them leaves you more exposed then meeting them, unless you have a very strong technical justification/experience (all provable) to roll-out in your defence and counter the prosecutions 'technical' experts! (Ive seen the defence hammered once by a technical expert and it wasnt a pretty sight)
You pays your money and you takes your choice, but if I was infront of the beak in a British court of law I think Id prefer to be relying on hanging my hat on having met BS7671, in whichever way you want to interpret it .......
This is an update from a company that provides an electronic PIR (as it was known) form that was updated to get rid of a glitch where using RCBO's defaulted the requirements to 1667ohms.. the amemdment now flags rcbo's on a TN system that do not meet requirements in accordance with 41.3.
http://blog.pirform.co.uk/post/2009/12/18/RCD-additional-intelligence-added.aspx
Like we have been saying throughout this thread the 1667 limit is applicable to TT only and if your on a tn system then your rcbo has to meet requirements of table 41.3.
Ill dig deeper into the exact reasoning Ive already attempted to explain in my words but either way it reflects the message to the OP and some posters in that Zs should be met in a TN system and rcd protection is not a cheap fix it option to give you a get out of jail card.
We are taught many things at college and this subject only cam about in the 16th then to the 17th ... i trained on the 15th and have always researched all new regulations to their core... most just read and accept amendments without understanding the core reasons for them... this on my mind opens the flood gates to misinterpretation and good debates like this one....
I don't claim to be any kind of know it all and do sometimes surprise myself to what i thought i knew was wrong but it is down to interpretation and until you are challenged you can plod along happily unaware hence i think this level of debate is on forums like this is a good thing.. not to prove who knows it all but to get to know the core values on what is your work bible.
I have self taught all amendments post 15th edition but rather than a poor tutor I have several forums to check my thinking!
PIRform | RCD additional intelligence added
Home now and I dont have the BGB with me,but unless it has changed since the BRB the above statement is not true.
The reg in the BRB that applies if I recall is 411.4.9
If anyone has access to the BGB and can check if 411.4.9 is still there it would clear this up. If 411.4.9 has been removed since the BRB I will stand corrected.
yep....still there...
Not true.
411.4.9
Direct quote-
The NICEIC advises using Table 41.3 where the installation has been so designed that the overcurrent characteristics of the RCBO to BS EN 61009-1 are being used for automatic disconnection.
A cautionary note must be added here a Zs value that is under 1667Ω only ensures that in the event of an earth fault, the RCD or RCBO should operate. It does not confirm that the circuit is totally compliant with other requirements of BS7671:2008 (2011). For TN-S or TN-C-S systems a Zs value significantly above that required by 41.3 could indicate a high resistance fault somewhere in the circuit which, in turn, could pose a fire risk.
Also, where an RCD is used for automatic disconnection because of high Zs readings, it must be confirmed that the L-N loop impedance is low enough to ensure that the overcurrent protective device operates before thermal damage occurs to the cable.
Yes the regulation does allow such a scenario i must admit but if you challenge any design body or scheme provider the above advice will be similar ..in a TNS or TNCS system using a rcd to satisfy a high Zs value should be done with extreme caution and not as a matter of routine.. again ill stress a circuit with a high Zs on a TN system should be investigated and measures taken to reduce this... suggesting the OP should deliberately introduce a Zs not compliant to Table 41.3 because he has a fall back to table 45.1. is questionable advice.
Don't forget table 45.1 and the regs relating to it was introduced or amended only in the 17th edition and as most of us are old school who design to a previous stricter guideline that is still taught ...
Reg' 411.4.9 gives a buffer zone for when Zs to table 41.3 cannot be achieved (as its been argued its better than nothing hence its introduction) but it should be for good reason and not poor design because utilising this regulation should be a last resort not done by design choice.
We have said from the start ...
-Its a No NO to deliberately introduce a non compliant zs then to fall back on this reg... the first thing would be to try improve the reading to meet table 41.3
-Any circuit new to a TN system should be compliant to table 41.3 regardless -no excuses for poor design, if the Ze is high then account for this in design or enquire to the DNO -if it can't be lowered then yes we have the rcd/rcbo option to fall back on.
If you do an inspection and Ze or Zs is too high you should first establish why and try rectify high reading only then if its not an option and rcd cover isn't installed then you can revert to using this option to satisfy disconnection times ... but ensuring you don't have a fire risk.
Im not saying you cannot use this regulation im saying you shouldn't be applying it loosely to a TN system or questions really have to be asked why you haven't met Zs values in the first place.
Reply to Type D RCBOs in the UK Electrical Forum area at ElectriciansForums.net