This is an update from a company that provides an electronic PIR (as it was known) form that was updated to get rid of a glitch where using RCBO's defaulted the requirements to 1667ohms.. the amemdment now flags rcbo's on a TN system that do not meet requirements in accordance with 41.3.
PIRform | RCD additional intelligence added
Like we have been saying throughout this thread the 1667 limit is applicable to TT only and if your on a tn system then your rcbo has to meet requirements of table 41.3.
Ill dig deeper into the exact reasoning Ive already attempted to explain in my words but either way it reflects the message to the OP and some posters in that Zs should be met in a TN system and rcd protection is not a cheap fix it option to give you a get out of jail card.
We are taught many things at college and this subject only cam about in the 16th then to the 17th ... i trained on the 15th and have always researched all new regulations to their core... most just read and accept amendments without understanding the core reasons for them... this on my mind opens the flood gates to misinterpretation and good debates like this one....
I don't claim to be any kind of know it all and do sometimes surprise myself to what i thought i knew was wrong but it is down to interpretation and until you are challenged you can plod along happily unaware hence i think this level of debate is on forums like this is a good thing.. not to prove who knows it all but to get to know the core values on what is your work bible.
I have self taught all amendments post 15th edition but rather than a poor tutor I have several forums to check my thinking!