In domestic when the Zs easily low enough why do we default to have type B instead of C curve MCB's/RCBO's
I don't think designed more suitable for the load.Type B is designed for domestic use.
Type B is designed for domestic use.
In the days of predominate tungsten lighting I always fitted C 6A on lighting to prevent nuisance tripping from a failing lamp. B or C is mindset providing ADS is provided it is totally irrelevant.
Both will trip in the same time if the current is enough to cause instantaneous operation.Type B will respond better/quicker to an overcurrent so surely the better option when you don't have to allow for inductive loads or startup current for example.
I don't actually know what you mean.Ok. Not soley for domestic but you know what I mean.
There is little in a domestic that requires a Type C.
Installing MCBs that trip at 5-10 times the current rather than 2-3 times should not be installed unless required.
Having a few LED downlights will not require a Type C.
There is no line of separation between a so called domestic protective device and a device for other purposes, it is mindset.
The product standard is EN60898 or EN61009 it is the type characteristics which define the intent.Are the different product standards not a line of separation ?
The product standard is EN60898 or EN61009 it is the type characteristics which define the intent.
The product standard is EN60898 or EN61009 it is the type characteristics which define the intent.