In domestic when the Zs easily low enough why do we default to have type B instead of C curve MCB's/RCBO's
 
In the days of predominate tungsten lighting I always fitted C 6A on lighting to prevent nuisance tripping from a failing lamp. B or C is mindset providing ADS is provided it is totally irrelevant.
 
Type B will respond better/quicker to an overcurrent so surely the better option when you don't have to allow for inductive loads or startup current for example.
Both will trip in the same time if the current is enough to cause instantaneous operation.
It’s only the thermal side where a difference would be noted.
 
Ok. Not soley for domestic but you know what I mean.

There is little in a domestic that requires a Type C.

Installing MCBs that trip at 5-10 times the current rather than 2-3 times should not be installed unless required.

Having a few LED downlights will not require a Type C.
I don't actually know what you mean.
 
I think a lot of it is down to availability too. We buy what the wholesalers have in for domestic stock. The wholesalers will be supplied with the devices that the manufacturers supply for domestic use.
This is generally a range of 6kA B curve breakers. You would have to specifically design for and request a C curve usually.

For instance Hager only do B curve mcbs in their 6kA range, and their reduced height RCBOs (aimed at consumer unit installation) at 6kA are all B curve.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Type of MCB .........................
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
Toneyz,
Last reply from
TJ Anderson,
Replies
25
Views
3,343

Advert

Back
Top