Hi there,

We have had an electrician work on a fix price job to rewire the house. He has routed all of the cabling under the bathroom floor. I expected that he would routed another way which was more difficult, but wouldn't have gone under the bathroom floor.

Is anyone able to confirm if this is A safe and B legal and up to regs. It doesn't feel right that all of the new circuits run under a area such as bathroom. Thinking what happens if there is an escape of water?

Many thanks

Rob
 
This should be perfectly fine. There should be no problems even in the event of an escape of water as the cable runs should not have any joins in them that could be affected by water ingress. Even if water ingress did cause problems to any part of the wiring system a rewire will have incorporated the most up to date circuit protection devices which are designed to prevent dangerous problems.

There are no regulations I can think of that have broken in this method. I would put a light fitting in the room under a bathroom with no worries at all.
I do believe your worries are unfounded.
 
If you are worried about a sudden escape of water then just make sure that your plumber is better than the Spark - everything will be fine then!
Agree with above - no regs. All underfloors are transit areas for cable runs, it’ll be RCD protected as of 18th edition.
 

Reply to Under bathroom floor rewire? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Article
This is an RSS feed of thread: Changing from system to combi boiler with under floor pipework. Content of the thread: Wondering should i change a...
Replies
0
Views
211
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top