E

ed-ectrician

I was doing some outdoor lights for someone and they asked me to look at their underfloor heating. You know how it goes!!

The problem is it seems to keep cutting out and then the controller which has timer and stat on it keeps resetting itself. No trip on rcd or mcb when this happens. Ok, sounds like it's either dodgy connection somewhere, IR fault or faulty controller. They have an identical one on separate circuit nearby which works fine so i took off the controller from that and put it on in place of faulty one. Still doing the same thing! So i check soundness of connection in DP switch between faulty controller and the board. All fine. Then i IR tested from board to controller (disconnected) with switch on still no joy. Even shorted switch out and IR tested the whole lot and tested to see if controller worked with switch shorted out. Still no joy. Looked at soundness of connections in DB. All ok.

Did end to end on underfloor heating cables. 24 ohms, sounds right.

I feel like i've exhausted the possibilities. Anyone else got any ideas?!!

Thanks
 
Have you tested the floor probe that's set in the floor? Sometimes with UFH programmers if they don't sense that the probes working they switch off, then try to reset. I know timeguard controllers do this.
 
Last edited by a moderator:
By the way, this is a sub question but if i cant solve this i've spent 3 hours on it so far, will prob spend longer as my pride is at stake here!!!!

I feel like a right 'see you next tuesday' billing for this time if it's not sorted. What would you do?!?!
 
You need to review the whole circuit and mat again.

You have a 30mA RCD protected circuit a 16A MCB a 6mm² cable (single radial I assume) connected to a switch of some sort and then to a power backbox (connected correctly? the power back box should not be able to take 6mm² cables) then the controller is fitted on the back box (how is the controller set up? Are there jumper switches? what are the displays if any on the controller on start up?) the controller is designed to take no more than 16A.
From the power box there are three pairs of wires each pair going to one of three underfloor heating mats (in the same room?), there are some unused terminals for a floor sensor (possibly) and (possibly) a pilot wire terminal unused.
There is no floor sensor (is the controller temperature sensor clear of dust and debris)
The floor heating mats appear to be 2 x 2.2kW and 1 x 6.6kW(really?), it is not known if there is an earthing grid associated with the mats, make of the mats is unknown.

There does not appear to be an earth fault as the RCD does not trip.
The current anticipated would trip a 16A MCB in about 10 seconds. The measured current on start up is not known.
The controller has been working for 2 years satisfactorily but has (in the last ....days) stopped working and when powered up starts and then cuts out, then starts, then cuts out...... (possibly not calling for heat yet and so not tripping MCB, but MCB was holding when it was working, is the controller staged i.e. only powering the mats by PWM or such like)

The heating mats have individual continuity on each (24, 24 , 8 ohms).
The insulation resistance of the mats is unknown.
The insulation resistance of the circuit up to the power box with and without the switch is OK.
The controller and power box from another location, where they are working, have been used in place of the original and the fault recurs (so the fault is not in the controller or back box).
The instructions state that when using a contactor (not used in this instance?) a snubber should be fitted across the load terminals.
When each mat is connected individually the fault recurs (so not a current loading issue)(only a triple fault on every the mats or a cross connection between the mats could cause this if the fault is in the mats.)


[Right no faults on fixed wiring, controller or mats (except loading), your heating is fine madam, that will be ÂŁ250, oh yes the resetting? it is typical of these units, just ignore it, that is what I am going to do!:nonod:]



Does the controller start up OK without the mats connected?
Does this controller work in the other location?
Do you have the specs / instructions for the controller, power box or mats that you can compare to current readings?
Did anything change just before the heating failed (any work DIY or Professional)?


Well I give up!
 
I know it's a simple thing but has the programmer been set to remote stat and not on floor probe mode, sorry you've probably been there for hours going through every permutation so this is probably a moot point.
 
Last edited by a moderator:
i think I might just keep repeating "It's not your fault" over and over again until she cries...

not your fault (Good Will Hunting) - YouTube

Seriously though I think it's ripping up floor and rewiring time....

Far too much load on one 15a controller anyway, it's no wonder it's not working for one reason or another. I can bill for my fault finding and advise to rewire. I'm not doing it though, sounds like a right pain in the arse and I'm too busy haha!

Seriously everyone thanks LOADS (pun?!) for your help on this. It makes me feel better knowing I have tried all the likely things and done what you guys would've done too. Makes me feel like less of a failure :)

Ed
 
I know it's a simple thing but has the programmer been set to remote stat and not on floor probe mode, sorry you've probably been there for hours going through every permutation so this is probably a moot point.

Yeah I checked this, thanks mate. I love pennywise too. And NOFX etc - reminds me of my youth! Went to see them all and lagwagon at deconstruction tour in east london when i was like 16 and a right little punker!
 
Yeah I checked this, thanks mate. I love pennywise too. And NOFX etc - reminds me of my youth! Went to see them all and lagwagon at deconstruction tour in east london when i was like 16 and a right little punker!

I only got to see Pennywise once with Jim Limburg still fronting them and a couple of times since with the new guys, it's not the same :( having said that the new singer sounds like dexster holland so it's should be the perfect combination of the offspring and Pennywise but it just doesn't work :(. I saw NOFX this year at download festival very funny and always good. Hopefully bad religion will be touring next year :)
 

Reply to Underfloor heating mystery... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K
  • Question
Thanks all. Sounds like I hadn’t completely missed the point on what Part P needs at least. I’m not so much worried about a knock on the door as...
Replies
4
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top