Can anyone help am looking for a diagram I have an splan system with an extra valve for the u /f heating
 
trigger the ufh valve from ufh stat. use valve microswitch to fire boiler via the stat input terminal in boiler (and ufh pump if fitted)
 
trigger the ufh valve from ufh stat. use valve microswitch to fire boiler via the stat input terminal in boiler (and ufh pump if fitted)

You shouldn't connect a dedicated ufh pump directly to the boiler sw live or else it will run when either of the other valves are open regardless of whether the ufh valve is open or not.
Connecting the boiler fire signal from the valve to the pump and the coil of a relay and use the relay to switch a live to the boiler.
 
You may need a pair of relays to stop back feeding from when one system calls everything will turn on. If a plumber isn't involved be aware of the UFH running temperatures compared to a system with radiators on. If this has already been thought about please excuse me!!
 
Pair of relays? If the underfloor has its own pump he'll need one relay to isolate it from the boiler switched live as I described above, why do you need a second relay to prevent backfeed?

If it was necessary to isolate the pumps so that the normal pump doesn't run whilst the ufh is on its own then you'd need a second relay. But that's a whole other matter and I've heard many arguments for and against that one.
 
I was thinking along the lines that if there is a pump for existing loops for the radiators, theirswitch wires would need to be separated through a relay or two depending on the setup of the system as they could just be trying to pump against a closed zone valve.
 
I was thinking along the lines that if there is a pump for existing loops for the radiators, theirswitch wires would need to be separated through a relay or two depending on the setup of the system as they could just be trying to pump against a closed zone valve.
then again, the ufh valve will be open so the pump will pump through that.
 
Even if there isn't a manifold controller (i.e. the UFH is a single zone) is there any reason why its stat output can't feed the UFH pump and valve motor? In this case the valve microswitch can simply be paralleled with the others to feed the boiler s/l without backfeeding.
 
Even if there isn't a manifold controller (i.e. the UFH is a single zone) is there any reason why its stat output can't feed the UFH pump and valve motor? In this case the valve microswitch can simply be paralleled with the others to feed the boiler s/l without backfeeding.
that's how i'd do it. then if it worked, fine. if not, back to the beermat for a revised diagram.
 
Even if there isn't a manifold controller (i.e. the UFH is a single zone) is there any reason why its stat output can't feed the UFH pump and valve motor? In this case the valve microswitch can simply be paralleled with the others to feed the boiler s/l without backfeeding.

I often find them wired this way, it is the simplest way of doing it, but then you've got the pump firing before the valve opens. It will shorten the life expectancy of the pump. A relay is the only option if you want the UFH valve to open, then the UFH pump and boiler to fire, but keeping the UFH pump control seperate from the main pump.
 
surely if the pump is triggered by the valve microswitch when the valve opens, that sorts the problem.

But the boiler is also triggered by that microswitch, and the main pump, which means you'll have backfeed from the DHW or CH when they are energised firing up the UFH pump when it's valve is closed. The only two options available is to put the UFH pump on the valve feed (not ideal), or on a relay operated from the valve's orange
 

Reply to Underfloor heating via an s plan system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Unfortunately I don't think you will get an "off the shelf" diagram for the system you are trying to do The Wiser system is very adaptable but it...
Replies
1
Views
497
  • Question
Update... I wired up my first heating system today! Thanks to all the help in this thread, (and the initial thread) I was completely prepared...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top