hi just some quick advice please guys, im working on a lampost circuit and the lamposts have been half buried so the inspection cover is underground, ive dug around one removed the cover and there is no fuse for the light, can I terminate the SWA cables in a steel box and put a IP68 plastic box inside of this and fuse the live then put the whole box just below the surface under the flag stone? or is there a better way cheers guys!
 
Lamposts have a colour scheme on the actual post...the bottom 12inchs is normally a light grey - it's the point that should be flush with the ground. The inspection panel shouldn't be underground. Im guessing they must be old lamposts....

LAMP POST CUT OUT LUCY 25 AMP LIGHT CONNECTION UNIT 6A FUSE | eBay

Thats the sort of thing you should really be terminating into...a lampost connection unit. That's if you can dig far enough to work comfortably.

Failing that then yeah you're going to have do it the way you said in a buried IP rated box...not ideal really imo, but what can you do...
 
As an eBay Associate we earn from qualifying purchases.
Is putting the box with the fuse and everything in just under the flagstone still classed as accessible if the fuse blows, or will i nee to put it all in some kind of inspection pit like an earth rod pit?
 
Well who was the clever bugger that mounted the posts so that the access cover is part underground?? All i can say, is be prepared for excessive corrosion and condensation inside that lamp post. ...Plump crazy!! lol!!
 

Reply to underground lighting cables in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
😄 It wasn't the worst I seen over the weekend. Took the kids to Cumbria zoo whilst over there, and the toilets by the giraffes just had twin...
Replies
7
Views
1K
hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
328

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top