Not contracting anymore, but 16th iee regs section 547-02-01 table 54h, cant of changed.?

Under the 16 th and 17th the selection from the table is
Live of 1mm to 16mm is equal size cpc
Live of 25 or 35 is 16mm cpc
Live of over 35mm is cpc >\= 1/2 size of live

Or it can be calculated by the adiabatic.

The commonly accepted size for a 100A service is 25mm tails with 16mm earth
 
I thought the 4mm was the earthing conductor and the OP was worried because it was smaller than the main bond.

If 4mm is satisfactory as the earthing conductor - which we don't know yet - then only a 2mm bond is required but 6mm being the minimum allowed.

But you are taking the cpc for the distribution circuit as the earthing conductor. It is the main earthing conductor at the intake which will determine the size of the main bonding conductors.
 
Ok, but even that is determined by the adiabatic regardless of what is actually fitted.
So, we would need to know the DNO fuse rating and the Ze.

There is a 10mm bond fitted anyway.

However, it is the 40A distribution circuit CPC that the OP is worried about.
 
The main earthing conductor on a TN-S system is the conductor between the cable sheath on a PILC cable or the earth conductor within a split concentric cable to the MET. From the MET they will be earthing conductors or CPC's and main bonding conductors...
 

Reply to Undersize earth conductor in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
527
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
505
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top