Hi All,

I am a little confused, probably something I am missing.....

I have just wired in a 7.4kw Neff V57THQ4L0 N70 Vented Hob. I ran a supply of 6mm from the board for the hob. My confusion is why the manufacture has provided a 1.5mm cable for me to wire this into the cooker connection unit. Is this common practice? Isn't the cable provided from the manufacturer massively undersized?

Many thanks
 
Yes. It’s common practice.

We are trained to use diversity with high loads, and take the rated full load of the appliance….

However, the hob itself may have electronic load management built in… it will never take the full load, or anything near the CCC of the cable
 
Can you post the installation instructions? Can’t find them online.
 
Yes. It’s common practice.

We are trained to use diversity with high loads, and take the rated full load of the appliance….

However, the hob itself may have electronic load management built in… it will never take the full load, or anything near the CCC of the cable
Ok thanks for confirming. I wasn’t aware of this. Many thanks
 
Is it a 5 core with parallel L+N? This is quite a nifty solution imo and far nicer to work with than 4mm flex.

If the hob is 7.4kW rated it won't be managing the load down from that, I've seen 5 ring hobs that manage the load to 3 kW, complete with plug top, complete junk IMO.
 
I've always wondered why more use isn't made of parallel runs.
I guess it's normally only really worth while for larger things. It's much easier to run 2x 150mm2 4 core SWAs than 1x 300mm3 SWA for example. The cable costs are higher buying 2 cables but if it saves a lot of effort or the routes are difficult for stiff cables it is worth it. On a smaller scale I do have a 4H4 MICC feeding a small single phase distribution board in my house, with the conductors paralleled, though this was mainly as the cable was to hand. The main drawback is it's a big problem if one core gets disconnected.
 

Reply to undersized cable provided by electric hob/cooker manufacturer? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I would run a new cable from the cooker switch down behind the cabinet to the outlet.
Replies
11
Views
4K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K
  • Question
If multiple socket outlets are connected via one length of 2.5mmsq then it is not protected against overload by the 32A device in the CU. (You...
Replies
1
Views
2K
  • Question
Personally I'd always fit 6mm. There was a thread on here a month or two ago where an electrician had run 4mm on a 32A breaker, another...
Replies
6
Views
3K
  • Question
agree with above. plug and play. once you got the hang of it.let 'erindoors have a go. then you may need an electrician.🤣😘
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks