A while back a had an issue with a commercial install I had done for a family members unit
Long story short, 5x50w led floods controlled by 4 robus PIR detectors. Also a 3 way switch for option to turn off, perm on and PIR sensors.
I tested the circuit prior to any work and all the readings where good. I came across an issue where the RCD FCU that I had used on the perimiter trunking kept tripping. Unfortunatly I ran out of time on the original install.
I went back just before xmas to finish a few snags on other works and to look at this fault.
Disconnected the load from the JB and all my works tested fine. Good Zs and I/R over range.
Tested the circuit back to the board and gor a dead short between all conductors. Checked the board and there was 3 outgoing lives from the MCB. I should have confirmed this before I originally installed anything but all the figures were good so I thought it was safe to proceed.
I confirmed the line, neutral and cpc for the lights I have installed. The others I could not confirm so put them in a little JB next to the DB with a label.
The problem I have is I could not I/R test with the others disconnected because there was 20v on the circuit and my tester would not test. As soon as you reconnect the other 2 outgoing line and neutrals the 20v disappears and I can test but get a dead short. I tried line and neutral to earth and that was a dead short also.
I dont understand what was going on. I have left it for over the xmas period as they are closed however I'm still scratching my head.
Any help would be really appreciated.
Long story short, 5x50w led floods controlled by 4 robus PIR detectors. Also a 3 way switch for option to turn off, perm on and PIR sensors.
I tested the circuit prior to any work and all the readings where good. I came across an issue where the RCD FCU that I had used on the perimiter trunking kept tripping. Unfortunatly I ran out of time on the original install.
I went back just before xmas to finish a few snags on other works and to look at this fault.
Disconnected the load from the JB and all my works tested fine. Good Zs and I/R over range.
Tested the circuit back to the board and gor a dead short between all conductors. Checked the board and there was 3 outgoing lives from the MCB. I should have confirmed this before I originally installed anything but all the figures were good so I thought it was safe to proceed.
I confirmed the line, neutral and cpc for the lights I have installed. The others I could not confirm so put them in a little JB next to the DB with a label.
The problem I have is I could not I/R test with the others disconnected because there was 20v on the circuit and my tester would not test. As soon as you reconnect the other 2 outgoing line and neutrals the 20v disappears and I can test but get a dead short. I tried line and neutral to earth and that was a dead short also.
I dont understand what was going on. I have left it for over the xmas period as they are closed however I'm still scratching my head.
Any help would be really appreciated.