My assessor said that the minimum CSA for a Main earthing conductor for a TT was 16mm. I questioned this as I thought it was 4mm.

Regulation 542.3.1 states every earthing conductor shall comply with section 543.

Section 543 refers mainly to the adiabatic (reg 543.1.3) or reg 543.1.4 (table 54.7), so if the CPC meets the adiabatic then its ok.

The on site guide even has a Table ( 4.4(ii) ) on page 41 (green copy) showing that 4mm is acceptable for a TT. I'm assuming this is from 543.1.1.

The assessors justification for the 16mm on a TT was that there is a diagram in OSG showing the CPC on a TT with 16mm written next to it (see page 16, fig 2.1(iii) - green OSG). Also the Electricians guide to the building regs - reprinted 2012 version (Table 3.3.2b - page 40) clearly shows that a 16mm CPC is required for a TT (assuming 25mm tails)??

How do you guys read the regs with regards minimum size CPC for a TT?

Also, just as an aside, why do we always have to have 16mm CPC for PME or TNS? If the regs say we can use EITHER reg 543.1.3 OR 543.1.4 why cant we just use the adiabatic (reg 543.1.3) and perhaps use a 6mm if it meets the reg?
 
When I had my assessment I was asked what the minimum size was for an earthing conductor (and no clarification on type of earthing was forthcoming) and the assessor was non plussed and confused when I said 2.5mm².
However this was the correct answer; as far as I am aware the absolute minimum permitted for an earthing conductor is 2.5mm². This would necessitate the conditions referred to above: A TT system where the earth rod current will not overload the conductor and the conductor is copper, mechanically protected and sheathed.
The discussion then went on to say that they wanted to encourage installers to use 16mm² in all cases as it was safer and accounted for changes that may be made to the installation, which, frankly, was utter rubbish.
 
When I had my assessment I was asked what the minimum size was for an earthing conductor (and no clarification on type of earthing was forthcoming) and the assessor was non plussed and confused when I said 2.5mm².
However this was the correct answer; as far as I am aware the absolute minimum permitted for an earthing conductor is 2.5mm². This would necessitate the conditions referred to above: A TT system where the earth rod current will not overload the conductor and the conductor is copper, mechanically protected and sheathed.
The discussion then went on to say that they wanted to encourage installers to use 16mm² in all cases as it was safer and accounted for changes that may be made to the installation, which, frankly, was utter rubbish.
How can they even push this rubbish out to contractors is beyond me.
Do they work to a different standard?
 
The discussion then went on to say that they wanted to encourage installers to use 16mm² in all cases as it was safer and accounted for changes that may be made to the installation, which, frankly, was utter rubbish.

This kind of one size fits all, paint by numbers, no thinking approach just can’t work for electrical installations.
It’s going to lead to customers being ripped off for unnecessary ‘upgrades’ and occasionally could lead to undersized protective conductors.
 
Was the assessor a Electrical Trainee type assessor, who could only look at diagrams and take
How can they even push this rubbish out to contractors is beyond me.
Do they work to a different standard?
As long as you don't question what they say, they will, get them to prove what they say, it may take some time but you may be surprised with the results, I'm waiting for all the Dumb's, Disagrees or whatever frankly say what you like I'm not bothered, far to long in the tooth to worry about peoples thoughts, until someone stands up to the BS they tell they will carry on taking your hard earned.
 
I see you are with Stroma @happyhippydad I havent had this conversation with the local NICEIC assessor, but when ever I question what the assessors or other such folk say, I say can you show me where that is in the books so I can read up on it later. They quickly move on! Similar things happens with building control poking there noses in when doing visits.
 
I said I'd be back with reg no

Yet again a contradiction.

On site guide table 4.4(iii) states the 4mm

Under neath in notes the contradiction :
The main protective bonding conductors shall have a cross sectional area not less than half that required for the earthing conductor and not less than 6mm.

So the main protection bonding conductors have to be min6mm and its ok for earthing conductor to be 4mm or even 2.5mm.
Shirley the earthing conductor should have the path of least resistance.

Have I interpreted that correctly?
I hope not.
 
Yes Pete, you have.

The earthing conductor and bonding conductor serve completely different purposes.

The former is there to carry current and is sized accordingly, the latter is there to equalise potential and is sized accordingly.

It's perfectly reasonable to expect that on many TT installations the bonding conductor/s will be larger than the main earthing conductor.
 
I have got to admit I didn't know this. Though with the explanations given I totally understand why.

I don't know why I didn't know it.

Anyone else out there didn't know it also? Go on admit it.

Or is it just me and the assessors?

Thanks
 

Reply to Understanding minimum CPC requirements? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top