HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,295
Reaction score
6,535
Location
Gloucestershire
I am in the process of hunting for another difficult fault (intermittent tripping RCD, absolutely no faults showing on any circuits and only 2mA fault current in Main earth).

My question does indirectly relate to this... perhaps.

When testing the RCD with my megger 1731 I am not getting a reading in mS. All I get is 'trp'. The RCD trips, but it does it so quickly and just states 'trp'.

The above was testing at a socket so I tried testing at the RCD itself and got the same.

The RCD is protecting 3 circuits, 2 socket circuits and the cooker. When i test at the RCD with the 3 breakers up the RCD trips and says 'trp'. When I switch off the cooker breaker and test I then get a proper reading (27mS). When I switch the sockets off and the cooker on I get a proper reading also (27mS). What does this mean?

Reading through the megger download does not give any useful info. It just says (under RCD testing), "if the RCD trips it will show 'trp'!!!!! (see pic below)
[ElectriciansForums.net] Understanding what this means on the megger 1731
 
I was assuming it was an 'auto' test where it does 0.5x, 1x & 5x in sequence, which is how I usually use mine. I think this will display TRP if it trips on 0.5x. If you were on the fixed 1x range then I expect the tester produces a small amount of 'leakage' while synchronising its test current injection circuit to the mains waveform, and even that is enough to push your RCD over the limit.
 
only 2mA fault current in Main earth).

When i test at the RCD with the 3 breakers up the RCD trips and says 'trp'. When I switch off the cooker breaker and test I then get a proper reading (27mS). When I switch the sockets off and the cooker on I get a proper reading also (27mS). What does this mean?

A measured current in the earthing conductor means very little, this kind of current can be measured on an installation with no faults at all.
To measure earth leakage you need to measure the imbalance between current in all live conductors, this is done by clamping around all live conductors at once.

Those test results suggest that the RCD is fine, but that there is earth leakage on both of those circuits which is biasing the RCD to trip at a lower current than it should.
 
A measured current in the earthing conductor means very little, this kind of current can be measured on an installation with no faults at all.
To measure earth leakage you need to measure the imbalance between current in all live conductors, this is done by clamping around all live conductors at once.

Those test results suggest that the RCD is fine, but that there is earth leakage on both of those circuits which is biasing the RCD to trip at a lower current than it should.
Thanks for this informative reply.
When you say clamp around all live conductors at once do you mean both the supply live and neutral? If so, why will this reading be different to clamping the main earth and bonding conductors?
Any difference shown when clamping the supply live and neutral would suggest earth leakage. Doesn't this current leak through either the main earth or the bonding conductors?
 
Thanks for this informative reply.
When you say clamp around all live conductors at once do you mean both the supply live and neutral? If so, why will this reading be different to clamping the main earth and bonding conductors?
Any difference shown when clamping the supply live and neutral would suggest earth leakage. Doesn't this current leak through either the main earth or the bonding conductors?

Yep, round both incoming Line and neutral. This wil show the imbalance, in other words leakage.

In theory clamping all bonding conductors and main earth should be the same thing, however this will never actually be the case. Some current can stray elsewhere, through pipes past the bonding conductor into the actual ground, moisture to ground etc...
 
In an ideal world it would yes, but in reality some will flow elsewhere too. Parallel paths, fortuitous connections to earth or even the fault you are trying to find could be diverting the leakage current elsewhere.

I imagine the easiest way of imagining it is a bonding conductor connected to a pipe for example, is just a potential divider.
 
When you say clamp around all live conductors at once do you mean both the supply live and neutral? If so, why will this reading be different to clamping the main earth and bonding conductors?
Both live conductors will have magnetic influence on each other due to current draw but these are cancelled out by each other. If there's some leakage going a different route there will be a part of the magnetic field that isn't cancelled out giving you a reading.

I tend to test with all conductors clamped, both lives and earth, then just the live conductors. This gives a ball park figure of what is finding parallel paths and what is going back down the main earth conductor.
 

Reply to Understanding what this means on the megger 1731 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
699
davesparks
D
  • Question
Aico use the term Megger on their CU stickers
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top