I am in the process of hunting for another difficult fault (intermittent tripping RCD, absolutely no faults showing on any circuits and only 2mA fault current in Main earth).
My question does indirectly relate to this... perhaps.
When testing the RCD with my megger 1731 I am not getting a reading in mS. All I get is 'trp'. The RCD trips, but it does it so quickly and just states 'trp'.
The above was testing at a socket so I tried testing at the RCD itself and got the same.
The RCD is protecting 3 circuits, 2 socket circuits and the cooker. When i test at the RCD with the 3 breakers up the RCD trips and says 'trp'. When I switch off the cooker breaker and test I then get a proper reading (27mS). When I switch the sockets off and the cooker on I get a proper reading also (27mS). What does this mean?
Reading through the megger download does not give any useful info. It just says (under RCD testing), "if the RCD trips it will show 'trp'!!!!! (see pic below)
My question does indirectly relate to this... perhaps.
When testing the RCD with my megger 1731 I am not getting a reading in mS. All I get is 'trp'. The RCD trips, but it does it so quickly and just states 'trp'.
The above was testing at a socket so I tried testing at the RCD itself and got the same.
The RCD is protecting 3 circuits, 2 socket circuits and the cooker. When i test at the RCD with the 3 breakers up the RCD trips and says 'trp'. When I switch off the cooker breaker and test I then get a proper reading (27mS). When I switch the sockets off and the cooker on I get a proper reading also (27mS). What does this mean?
Reading through the megger download does not give any useful info. It just says (under RCD testing), "if the RCD trips it will show 'trp'!!!!! (see pic below)