Billwah

Hi there all,
Just had an EICR c/o in my 3 bed house, and got an unsatisfactory report with c2 and c3 observations.

The c3 is an advisory, with the two c2's causing the unsatis overall report.

The CU is 20 yes old and plastic, with RCD to some circuits, and not others. All are MCBs.

Have been advised to either replace CU for metal, containing similar breakers. OR replace RCD and MCB with RCBOs to eliminate the c2 codes.

One of the c2 codes is for no supplemental bonding.

Friend at work is going through his electrician training and thinks the 2 c2's could be c3s.

Any advice as to which is correct would be fantastic.

Bill
 
There is no such thing as a fire rated consumer unit.


I dunno....Went to this previous year...(mcbs cleaned before the pic was taken) contained the situation.

[ElectriciansForums.net] Unsatisfactory EICR??
 
Does the cooker circuit have a socket outlet on the plate?

If not It shouldnt really be a c2 because the lighting and cooker circuits are not rcd protected, as it was pre-regulation
Should be c3 with recommendation to upgrade surely
 
Looks like you've had a visit from the in the van testers. Should've taken half a day at least if done to the letter, t will not have been carried out with the attention they require. From what we can see here though he may be correct regarding the c2 for lack of supplementary bonding. Easy solution is to replace the bathroom lighting mcb for an rcbo.
 

Reply to Unsatisfactory EICR?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
718
I would add a price for an eicr. they are highly unlikely to put in writing that it must be satisfactory for the order to be placed.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top