M

mrmisior

the existing setup:
32A mcb, 2 x 2.5mm twin & earth cables in parallel (ring final?) from CU to cooker switch (40m length), there is no other sockets or spurs - only the cooker switch, 6mm cable from cooker switch to cooker (<2m lenght)
it is not right, is it? how can I make it right?
also: the mcb is marked 'heater' not 'cooker'...

Michael
 
with diversity applied, the current is generally <20A, so i can't see a problem.
the cooker unit would draw a maximum of 29A when all hobs and both ovens are on (and on maximum power).
in normal use it would be 1 oven and 1-2 hobs ~ 10-15A total.
thank you everyone for answers and suggestions.
cables are terminated at mcb and cooker switch and have plenty of breathing space around.
will leave it as it is.
 
If the cooker is only drawing the figures in the region that Tel has posted then it sounds fine.

This is nothing more than a spur off of a ring that is supplying nothing else and all the current is being pulled from the centre of the ring. Perhaps the old ring for the kitchen was used to supply the cooker whilst a new ring was installed for a new kitchen installation?

Surely suggesting a rewire of this circuit could only be made on an OPINION because certain sparks wouldn't be happy installing such a circuit in this manner. However, unless you can PROVE that it is unsafe then you can't really enforce the customer having to stick hand in pocket ;)

:thumbsup
 
for the peace of mind:
powered the cooker up with bottom oven on max 260 C degrees, top oven/grill on max. and 4 hobs on max. for about 20 minutes.
checked the cooker ring cables using instant thermometer in CU, in the middle of the run and at cooker switch - at all three points cables were at temperatures 25 to 27 C degrees.
to compare, other cables sockets ring, lights ring were at 20 C degrees at the same time.
Zs is 0.84 with B32 mcb.
thanks again everyone for pointing out possible solutions.
 
Using other than “standard domestic final circuits” legally requires the installer to prove it is safe (strength and capability) typically done with design calcs. Please calculate (at the worse place, a fault fed by both legs) at one “leg” phase to (1.5mm cpc) earth, typical a fauna/rodent damage.

The reason why only large multicore (not table 4D5 flat T&E) cables are run in parallel. (Even then, parallel is usually done for ease of physical installation as it is inferior electrically), and always lugged at terminations.

The withstand of final ring circuits was no good back in the day when flat 2.5mm T&E had only a 1.0mm cpc, cpc would not always withstand phase to earth faults and would “fuse”, your 5.0mm lives to 1.5mm cpc is worst still.

Standard Flat 4D5 T&E cable final ring circuits are not electrically perfect, to install we have many extra requirements to keep the right side of things.
 
i see the prophets of doom are awake. i fail to see why anything that is skightly unconventional should be ripped out as long as it complies with current regs.and can handle the load.

 

Reply to unusual cooker wiring? or wrong? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top