Been testing a modified circuit today.

Ze = o.20
R1 + R2 = 0.77
Zs = 1.77

So the reading is about 0.80 higher than I was expecting... Nothing on this (lighting) circuit switched on..... I was testing at the end of a smoke alarm addition.

I've read elsewhere, that its a good idea to do a Zs on the outgoing terminal of the RCBO to look for the "addition" this device is giving.

Is this correct? Anyone be able to point me in the direction of any previous threads, or guidance?

Thanks
 
I know a company that uses this..

Aerosol - ESC Electrical Contact Cleaner Spray - 500ml - [AT-1487] - http://www.thesafetysupplycompany.co.uk/p/8954323/aerosol---esc-electrical-contact-cleaner-spray----500ml---at-1487.html?gclid=CjwKEAjw4vzKBRCt9Zmg8f2blgESJADN5fDgvfGfr2lGv4q91BRXOKGuZVQs0qVr5sEUVOuKGhBU6RoCMKXw_wcB

on their supply leads in a factory.

I don't think you really need to worry too much about it though.

Fundamentally, it appears as if the protective devices are introducing significant impedances to question the effectiveness of your protective measure. If I was in that position (assuming I can personally verify the accuracy of my instrument) I would accept and record the readings measured. If these are too high I would try a replacement and would contact the manufacturer for their spiel, and maybe record it on the documentation.

Using calculation to compare your measured value, is for purposes exactly as you are demonstrating here. :thumbsup:

For the argument of referring to calculation instead...

Opting to refer to calculation over measurement would be naive. In a real world scenario, a fault current is going to flow down your measured impedance, not your calculated impedance. Calculations, while useful, never compensate for connection resistances, contact resistance or arc gaps.

Yes, the H&S world, Training courses, Guidance Note 3 and the incoming 18th edition all suggest EFLI can be verified by calculation with the measured protective conductor continuity and supply impedance loop. But these fault currents don't flow down imaginary numbers.

Also, the disconnection of a protective conductor when verifying continuity will remove the parallels. When we measure Zs we want the parallels.We need to start paying more attention to the pefc and pscc (and therein the pfc) within our circuits and not just at the origin or submains. The 18th edition is planning on introducing terms like:

  • rated short-time withstand current, Icw (already there)
  • rated peak withstand current, Ipk
  • rated conditional short-circuit current, Icc
These have been around for powertrack busbar systems but are now going to be more commonly used for any assembly. So we will need to set our testers to pfc (which means it will do an EFLI test and play with ohms law) and make sure all the parallels are there to ensure we measure the highest pfc value.
 

Reply to Unusual Zs reading when testing circuit with RCBO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
1K
OLDBOY
O
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K
The reason is that ADS is all designed around protection of the individual in the event of contact (nail into a cable shorting to earth/cpc sort...
Replies
11
Views
3K
  • Question
Have you double checked your busbar connections to make sure you haven't accidentally got the finger behind the main switch terminal?
    • Like
Replies
11
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks