Am I correct by saying if I install a new consumer unit, like for like replacement with no additions I don't have to upgrade main protective bonding conductors if they are 6mm, aslong as there's no signs of thermal damage. Tnc-s system.
Would I note this on departures on electrical installation cert.
 
Hi Mick, This is from ESC best practice guide for "Consumer unit replacement in domestic and similar premises"

"A 6 mm main protective bonding conductor size could be

deemed adequate where the minimum size required by

Regulation 544.1.1 of BS 7671 is 10 mm if the bonding conductors have been in place for a significant time and show no signs of thermal damage"
 
Hi all

Am I correct by saying if I install a new consumer unit, like for like replacement with no additions I don't have to upgrade main protective bonding conductors if they are 6mm, aslong as there's no signs of thermal damage. Tnc-s system.
Would I note this on departures on electrical installation cert.

It is not like for like is it? So this reason is wrong. But yes you can leave 6mm in place for other reasons you stated and if it satisfies adiabatic equation and 10mm protective bonding is in place for TN-C-S
 
Last edited:

Reply to upgrade in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
952
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top