M
m1ck_b87
Hi all
Am I correct by saying if I install a new consumer unit, like for like replacement with no additions I don't have to upgrade main protective bonding conductors if they are 6mm, aslong as there's no signs of thermal damage. Tnc-s system.
Would I note this on departures on electrical installation cert.
Am I correct by saying if I install a new consumer unit, like for like replacement with no additions I don't have to upgrade main protective bonding conductors if they are 6mm, aslong as there's no signs of thermal damage. Tnc-s system.
Would I note this on departures on electrical installation cert.