If TNCS then i would have thought your assessor will be looking for 16mm earthing conductor in case of a lost neutral on the suppliers network.
And why would the method of supply dictate the size of the main earthing conductor???
Apologies, I thought my OP mentioned it was a PME supply, but I hadn't.
It is of no consequence what the method of supply is, your main bonding conductors are 10mm so all you need is an adiabatic to confirm that the csa of the main earthing conductor is adequate.
Because that was what I was taught and have been told by others electricians - if you change the board, you need to make sure that tails are 25mm and earth is 16mm to meet 17th Ed requirements. If that's not the case, then fine - lesson learnt!
Forgive me if I sound a bit harsh here but you would only have been taught this on a Electrical Trainee course, hence my hatred of the people who peddle these useless courses to the masses as all they do is preach myth and here say. I can assure you that no electrician would have told you that this is the case because real electricians can differenciate between the OSG and the BGB.
If I'm wrong, forgive me, but if I'm right and you're a Electrical Trainee yourself I would heavily recommend you spend the next few weeks taking your BGB to bed and spending a couple of hours a night on some bed time reading. Personally, I believe that a front to back knowledge of the BGB combined with the understanding of the type of circuits you are working on is all you need to be a good electrician.