The bonding the same. If you stay with the 10mm^ Main Earth Conductor then as per reg 544.1.1 you can fit fit a main bonding condutor that is not less than half the CSA of the Main Earth Elcectrode which is 10 so it can be 5mm^. But that reg insists on 6mm minimum so you can fit that. Again if you fitted the 16mm^ Main Earth then half that is 8mm^ which as there is no such cable size you up to 10mm^. Again as I'd have fitted the 16mm^ main Earth I would fit the 10mm^ bond.
If you were to install a 2 way CU with a main RCCB which had a max rating of 63amps, would you struggle and fit 25mm tails or take the easy road and fit 16mm tails?
It clearly state that the total demand of the main shouldn't be exceeded, so surely 16mm would be ok in a case like this
Cost yet again.
Re: upgrading meter tails
What has not been mentioned is the size of the fusing at the service head is it 60 or 80 amps?
You know the RCCB will not give you over current protection