SJD

-
Mentor
Arms
Joined
Feb 10, 2012
Messages
2,287
Reaction score
2,862
Location
Braccan heal
Background
A pool installation uses two single phase pumps to circulate the water (through a boiler, and filtering, dosing etc). The pumps are controlled via contactors in the pump house, plus a remote emergency stop close to the pool. The location is somewhat rural, and prone to power cuts, usually of a short duration. If there is a power cut, the pumps can be tripped until someone notices - usually when the pool is planned to be used - e.g. the next day or after several days. By which time the water can be too cold or out of spec re dosing etc.

Question
I've been asked would it be possible to put the pumps on a UPS, so short duration power cuts don't trip them. I can see issues with the contactors and emergency stop if not properly thought out, but that aside, I'm wondering about the UPS rating. The type label for the pumps is attached, but I'm thinking the UPS would need a somewhat higher rating (than 2x what is on the label) to cope with starting currents, but UPS specs are a bit beyond my expertise (I haven't a clue).

I'd also be interested in any comments as to why it might not be a good idea (I don't especially want to do it)!

[ElectriciansForums.net] UPS specification for pool pumps
 
If you put, say a 3kw ups on the whole lot, pumps, control and boiler (maybe the pool DB entirely)
It will sort out short duration cut’s however if it is long enough for the battery to deplete, it is still likely to trip something.
 
Perhaps it would be a better solution to have some sort of alarm that alerts people to a fault or out of spec. Temperature?
 
Perhaps it would be a better solution to have some sort of alarm that alerts people to a fault or out of spec. Temperature?
This might help sometimes, but if there is a power fail late Friday, and nobody is around till after the weekend, that is 2 to 3 days when the pumps maybe could have been running but weren't. Unless the alarm was sent to a mobile phone I suppose, and someone could then visit (which in itself might be an issue).
 
I think I'd be looking more at 6kw to run the whole lot.
And depending on the length of the power outages I'd be suggesting a generator if they were lengthy.
If you put, say a 3kw ups on the whole lot, pumps, control and boiler (maybe the pool DB entirely)

It was suggested to me to put the Pool DB on the UPS, there is not much unrelated connected (just a few lights, I think).
Total would be no more than 3kW (when running).

But do I need to then uprate the UPS (e.g. to 6kW or more) to cope with pump start-up currents? Or do typical (decent quality) UPS cope with start-up surges?
 
I hesitate to suggest this, but Is it too risky an idea to consider automatic restart of the pumps after power is restored?
I've heard of an implementation putting the nc contacts of a short delay period timer (eg a second or two depending on how cleanly power usually comes back) across the 'start' button for each pumps contactor.
This could be a stupid risky idea, or if it's electrically sound, it could be a cost-effective mod that the owner could 'switch in' when needed? 🫣
I would have thought the boiler would restart by itself, maybe once it sees flow, but is there other equipment that packs up as well, meaning you really do need UPS power?
 
For a UPS to run for possibly two days you are going to need some serious battery packs.
Agree completely, but I don't think that was the original requirement. The first post uses the phrase "short duration" twice when describing the power outages. The longer period is mentioned in the context of how long the setup stays off because it's tripped and nobody's noticed, or they are away!
 
I think firstly you need to figure out what it is that is tripping.

I would not expect a motor overload to trip because of a short power cut.

however depending on the type of boiler, it may go into "lockout" because the fan or burner blower has stopped.

it may be that just a small ups on the boiler itself will suffice.
if the pumps stop for a few seconds , the boiler may well shut down or reduce its output as the temperature increases but should start up again when it sees the temperature reduce when the pump starts again?
 
I think firstly you need to figure out what it is that is tripping.

I would not expect a motor overload to trip because of a short power cut.

however depending on the type of boiler, it may go into "lockout" because the fan or burner blower has stopped.

it may be that just a small ups on the boiler itself will suffice.
if the pumps stop for a few seconds , the boiler may well shut down or reduce its output as the temperature increases but should start up again when it sees the temperature reduce when the pump starts again?

No, it is power to the whole premises that loses power. It is a somewhat rural location, and prone to power cuts, mostly of a short duration, sometimes longer.

When the power cuts out, the contactors drop out, and when power is restored, someone needs to restart the pumps.

The boiler just restarts when power is restored, except with no water flowing, it then shuts down.
 
ah, this seems fairly easy to resolve.

There is no requirement for manual starting of pumps, just wire the pump contactors to come on with the boiler time clock.
if there is no time clock then add one.
 
FWIW. I manage a site with pool pumps etc etc. If grid is lost, there is a 20 second delay before genny powers up. UPS's are used for the internet and internal comms to enable reporting of what is going on. Because the genny is not powerful enough to power all possible loads, certain loads are held off until the grid is restored, this includes the many pool pumps. When grid is restored the pool pumps re-start automatically as they are controlled by manual selector switches , not push button start requests. You could just replace the push buttons with a selector switch - maybe.....
Either way the pool control panel was built by a professional outfit and the pumps always re-started when power is restored.
 
ah, this seems fairly easy to resolve.

There is no requirement for manual starting of pumps, just wire the pump contactors to come on with the boiler time clock.
if there is no time clock then add one.

The pumps have to be started manually for a few reasons, partly safety concerns (plus there is an emergency stop wired in at the pool), and partly because the pumps don't always reliably start (something to do with the pipe arrangements and one of them sometimes getting an airlock). So if they are stopped, someone has to start them and physically check in the pump house they both run.

Hence the site would like to eliminate the number of times they stop (with a UPS).
 
What safety concerns?
Why the emergency stop?
Pipe arrangements need work?
All the swimming pools I have been involved with re-start automatically once power is restored, it sounds as though the installation needs revising IMO.
 
What safety concerns?
Why the emergency stop?
Pipe arrangements need work?
All the swimming pools I have been involved with re-start automatically once power is restored, it sounds as though the installation needs revising IMO.
Some external safety review recommended adding an emergency stop, I suspect they thought someone might get sucked against a water intake, so one was installed. I've no idea whether this is a realistic concern or not, but not for me to question it!

Yes, I think the pipe arrangements are a problem, some pipework is above the pool and pump water levels. There are also quite a number of valves to allow things like backwashing of filters, filling, emptying. I think not all the pipework is fully water tight (there are minor leaks here and there).

However, the request is for a UPS to work with the system & pipework as it is, there is not the budget to revist these at this time, and beyond my expertise (I don't do anything that involves getting wet). It is a somewhat legacy system with alterations over time.

Possibly putting the pumps, boiler & any related items like dosing & monitoring on the one UPS. Given that the pumps run at approx 2kW, and the rest will takes less than 1kW, the total load is no more than 3kW. It only has to run for a short time for short outages (30 mins, perhaps even less).

My question is for people familiar with UPSs, do I just suggest a UPS rated at 3kW, or do I need to allow somewhat more to cope with pump start-up? Generally there will be mains power when the pumps are started, the UPS is just to keep them running, so possibly 3kW is sufficient?
 
Last edited:
Any UPS has to be the supply for the pumps, the grid runs behind it. Its the only real way of ensuring there is no interruption. a UPS can also be a grid conditioner and clean up a crappy grid. So your pumps start current will need to go through the UPS..... So any UPS you will need to check their specs for short duration current surge.
 
This sound like a very amateur bodge up DIY pool, personally it would give me the jitters on what else has been bodged, think I would walk away.
 
Any UPS has to be the supply for the pumps, the grid runs behind it. Its the only real way of ensuring there is no interruption. a UPS can also be a grid conditioner and clean up a crappy grid. So your pumps start current will need to go through the UPS..... So any UPS you will need to check their specs for short duration current surge.
Ahh yes, of course, thanks.
 
This sound like a very amateur bodge up DIY pool, personally it would give me the jitters on what else has been bodged, think I would walk away.
Professionally installed (I understand) some years ago, but perhaps not very well.

I quite agree that I'd prefer not to be involved, but do a lot of electrical work for the site and difficult to just say I can't help. Ideally I'd say get their pool company to specify what is needed, except they don't currently have one, just a plumber plus non-technical maintenance staff.

Edit: The more I think about this, perhaps I can have the site call a UPS supplier and give them the pump specs, then they get said UPS supplier to quote for a suitable model. At least then if the UPS proves insufficient, it won't be my problem!
 
Last edited:
Professionally installed (I understand) some years ago, but perhaps not very well.

I quite agree that I'd prefer not to be involved, but do a lot of electrical work for the site and difficult to just say I can't help. Ideally I'd say get their pool company to specify what is needed, except they don't currently have one, just a plumber plus non-technical maintenance staff.

Edit: The more I think about this, perhaps I can have the site call a UPS supplier and give them the pump specs, then they get said UPS supplier to quote for a suitable model. At least then if the UPS proves insufficient, it won't be my problem!
The both pools and spa where I work both have an alarm that also turns the pumps off and need to be manually reset, both are well sign posted, so I'm guessing it's a requirement for at least holiday lets. The spa and one pool I was directed to wire as such.

You could change the alarm button to a different type like push to break and twist to reset type ones, which would enable the pumps etc to restart after a power outage.

I wouldn't expect for airlocks to be a problem, as ours are often emptied of water when cleaning filters or using the vacuum pipe.

Another option is to use SMS device for monitoring and to maybe have remote reset.

The last thing I would be doing is using UPS i would be spending the money on repairing the leaky pipes.


Info:
Further detailed information on equipment such as slides can be found in the HSE
document referenced in the introduction.

Pool Outlets
In recent years there have been fatal accidents where persons, often young
children, have become trapped by the pressure on a pool outlet. It is important
that:
Where possible, at least two outlets, spaced a minimum of two metres
Apart should be provided to the suction line.
Outlet covers are secure, kept in good condition and tamper-proof.
Outlet covers are visually checked daily. On a regular basis, someone should
Also dive to carry out a more thorough check.

Consideration should also be given to providing an emergency stop button that
shuts down circulation pumps and associated equipment. The most serious
accidents occur with pools with only one outlet. If you have one outlet you
must seek the advice of a pool specialist on methods that can reduce the risk of
entrapment.
Pool Grilles
Any grille openings in the pool must be designed to prevent limbs and fingers
getting trapped. The size of any aperture should not exceed 8 mm, if this
dimension is exceeded, you should obtain advice on replacing the grille
 
Last edited:
The last thing I would be doing is using UPS i would be spending the money on repairing the leaky pipes.
I'm inclined to agree. My understanding is only one of the pumps has an issue with air locks, the other one doesn't, so I'd want to know why this is. However, a relatively new maintenance guy on site seems convinced a UPS is the way to go, and seems to have convinced the others of this as well.

I will be at the site on this coming week for other work, and will raise some of the points in the thread. I'm probably going to suggest they try and get the opinion of a professional pool maintenance company.
 
Some external safety review recommended adding an emergency stop, I suspect they thought someone might get sucked against a water intake, so one was installed. I've no idea whether this is a realistic concern or not, but not for me to question it!

Yes, I think the pipe arrangements are a problem, some pipework is above the pool and pump water levels. There are also quite a number of valves to allow things like backwashing of filters, filling, emptying. I think not all the pipework is fully water tight (there are minor leaks here and there).
Some year back there was a case of a young girl killed by being sucked down to the bottom of a pool when being emptied through the power drain point, these are now illegal in public pools, nonetheless this was not the water intake or skimmers.

Pools do not have pipework above the water levels, backwashing, filtering and emptying are all controlled by a multi way valve at the filter/filters, as I said its a bodge job, I am walking away I suggest you do the same.
 

Reply to UPS specification for pool pumps in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

  • Question
Super- very helpful.. thanks lucien
Replies
2
Views
903
The 4 pumps are :- 1. boiler to cylinder 2. C/H and UFH circulating pump 3. UFH dedicated pump after manifold 4. DHW circulating pump. (this just...
Replies
4
Views
2K
  • Question
If anyone else is interested in this pool expense saving article, PM me and I will send it, unless the mods can find a way to post an eight page...
Replies
13
Views
3K
  • Question
A good challenge is always a good learning experience
Replies
13
Views
2K
  • Question
The manufacturer describes slow deterioration of the insulation due to the motor running hot. There was never a gate valve fitted, there has been...
Replies
5
Views
4K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Trending Electricians Tools

New job, new tester; Megger 1741+, those that have one; anything good/bad to report? Work also trusting me with a Flir E5 magical heat-reading...
Replies
210
Views
95K
Absolutely correct they hold water, shrouds are totally unnecessary. 20s is 24mm spanner, 20 large is 30mm spanner.
2
Replies
41
Views
45K
If that little thing, plugs your butt, you better eat slowly. 🤣
    • Like
2 3 4 5 6 7 8 9 10 11 12 13 14
Replies
336
Views
41K
B
I'd say everyone has knowledge gaps in their area of electrical work I know i have quite a few i work on to fill them in
2 3 4
Replies
75
Views
29K
I too have been tempted.. I’m buying for my son. He’s in his2nd year at collage and looking for apprentiship. Sadly it’s almost impossible in my...
Replies
11
Views
25K
Of course. “Ye canna change the laws of physics” EDIT. oh blimey, I just spotted the date of the OP. ? Thank you very much @Lord lee jan You...
Replies
40
Views
23K
Only way to do it in a tight space
2
Replies
33
Views
21K
The display on the Mft pro is not very durable mine is broken already 😡
2
Replies
29
Views
21K
Only lawyers , solicitors and dodgy chat up lines charge for picking up the telephone 🙃
2 3 4
Replies
97
Views
20K
J
I'm not entirely certain as it's very tough, but brittle when cold.
2 3
Replies
65
Views
19K
nicebutdim
N

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks