Background
A pool installation uses two single phase pumps to circulate the water (through a boiler, and filtering, dosing etc). The pumps are controlled via contactors in the pump house, plus a remote emergency stop close to the pool. The location is somewhat rural, and prone to power cuts, usually of a short duration. If there is a power cut, the pumps can be tripped until someone notices - usually when the pool is planned to be used - e.g. the next day or after several days. By which time the water can be too cold or out of spec re dosing etc.

Question
I've been asked would it be possible to put the pumps on a UPS, so short duration power cuts don't trip them. I can see issues with the contactors and emergency stop if not properly thought out, but that aside, I'm wondering about the UPS rating. The type label for the pumps is attached, but I'm thinking the UPS would need a somewhat higher rating (than 2x what is on the label) to cope with starting currents, but UPS specs are a bit beyond my expertise (I haven't a clue).

I'd also be interested in any comments as to why it might not be a good idea (I don't especially want to do it)!

[ElectriciansForums.net] UPS specification for pool pumps
 
If you put, say a 3kw ups on the whole lot, pumps, control and boiler (maybe the pool DB entirely)
It will sort out short duration cut’s however if it is long enough for the battery to deplete, it is still likely to trip something.
 
I think I'd be looking more at 6kw to run the whole lot.
And depending on the length of the power outages I'd be suggesting a generator if they were lengthy.
 
Perhaps it would be a better solution to have some sort of alarm that alerts people to a fault or out of spec. Temperature?
 
Perhaps it would be a better solution to have some sort of alarm that alerts people to a fault or out of spec. Temperature?
This might help sometimes, but if there is a power fail late Friday, and nobody is around till after the weekend, that is 2 to 3 days when the pumps maybe could have been running but weren't. Unless the alarm was sent to a mobile phone I suppose, and someone could then visit (which in itself might be an issue).
 
I think I'd be looking more at 6kw to run the whole lot.
And depending on the length of the power outages I'd be suggesting a generator if they were lengthy.
If you put, say a 3kw ups on the whole lot, pumps, control and boiler (maybe the pool DB entirely)

It was suggested to me to put the Pool DB on the UPS, there is not much unrelated connected (just a few lights, I think).
Total would be no more than 3kW (when running).

But do I need to then uprate the UPS (e.g. to 6kW or more) to cope with pump start-up currents? Or do typical (decent quality) UPS cope with start-up surges?
 
I hesitate to suggest this, but Is it too risky an idea to consider automatic restart of the pumps after power is restored?
I've heard of an implementation putting the nc contacts of a short delay period timer (eg a second or two depending on how cleanly power usually comes back) across the 'start' button for each pumps contactor.
This could be a stupid risky idea, or if it's electrically sound, it could be a cost-effective mod that the owner could 'switch in' when needed? đź«Ł
I would have thought the boiler would restart by itself, maybe once it sees flow, but is there other equipment that packs up as well, meaning you really do need UPS power?
 
For a UPS to run for possibly two days you are going to need some serious battery packs.
Agree completely, but I don't think that was the original requirement. The first post uses the phrase "short duration" twice when describing the power outages. The longer period is mentioned in the context of how long the setup stays off because it's tripped and nobody's noticed, or they are away!
 
I think firstly you need to figure out what it is that is tripping.

I would not expect a motor overload to trip because of a short power cut.

however depending on the type of boiler, it may go into "lockout" because the fan or burner blower has stopped.

it may be that just a small ups on the boiler itself will suffice.
if the pumps stop for a few seconds , the boiler may well shut down or reduce its output as the temperature increases but should start up again when it sees the temperature reduce when the pump starts again?
 
I think firstly you need to figure out what it is that is tripping.

I would not expect a motor overload to trip because of a short power cut.

however depending on the type of boiler, it may go into "lockout" because the fan or burner blower has stopped.

it may be that just a small ups on the boiler itself will suffice.
if the pumps stop for a few seconds , the boiler may well shut down or reduce its output as the temperature increases but should start up again when it sees the temperature reduce when the pump starts again?

No, it is power to the whole premises that loses power. It is a somewhat rural location, and prone to power cuts, mostly of a short duration, sometimes longer.

When the power cuts out, the contactors drop out, and when power is restored, someone needs to restart the pumps.

The boiler just restarts when power is restored, except with no water flowing, it then shuts down.
 
ah, this seems fairly easy to resolve.

There is no requirement for manual starting of pumps, just wire the pump contactors to come on with the boiler time clock.
if there is no time clock then add one.
 
FWIW. I manage a site with pool pumps etc etc. If grid is lost, there is a 20 second delay before genny powers up. UPS's are used for the internet and internal comms to enable reporting of what is going on. Because the genny is not powerful enough to power all possible loads, certain loads are held off until the grid is restored, this includes the many pool pumps. When grid is restored the pool pumps re-start automatically as they are controlled by manual selector switches , not push button start requests. You could just replace the push buttons with a selector switch - maybe.....
Either way the pool control panel was built by a professional outfit and the pumps always re-started when power is restored.
 
ah, this seems fairly easy to resolve.

There is no requirement for manual starting of pumps, just wire the pump contactors to come on with the boiler time clock.
if there is no time clock then add one.

The pumps have to be started manually for a few reasons, partly safety concerns (plus there is an emergency stop wired in at the pool), and partly because the pumps don't always reliably start (something to do with the pipe arrangements and one of them sometimes getting an airlock). So if they are stopped, someone has to start them and physically check in the pump house they both run.

Hence the site would like to eliminate the number of times they stop (with a UPS).
 

Reply to UPS specification for pool pumps in the Electrical Tools and Products area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The 4 pumps are :- 1. boiler to cylinder 2. C/H and UFH circulating pump 3. UFH dedicated pump after manifold 4. DHW circulating pump. (this just...
Replies
4
Views
2K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top