I no theres a seperate feed for outbuilding surplies but need some urgent advice on wiring a d.b. and circuits in a newly built large shed, being used as an outbuilding.
The garage will have three circuits. One lighting wired in 1mm twin an earth on a 6a type b circuit breaker. One power in 2.5/1.5mm twin an earth on a 20a type b circuit breaker. One circuit powering a 3kw water heater in 2.5/1.5mm on a 16a mcb.
I was goin to run 2 core, 10mm swa cable from the main consumer unit to the garage d.b. part clipped direct to the external house wall and part burried and use the swa as main earth. The d.b. will have fault protection by the 80a rcd in the house consumer unit. I will terminate the swa in two metal boxes attached flush with the c.u. and d.b. using usual banjo method.
I was going to use a 42a type b in the house comsumer unit feeding the swa. The house earth arrangement is tn-s and has a Ze of 0.12 and PFC of 2.2 Ka.
My main query is do i need an rcd in the garage d.b. (if so what size) and whether anyone would wire this job differently. I have done the calculations using design current etc and as far as i can tell it is all above board, but would appreciate someone else checking or giving useful feedback.
Also please dont feel the need to remind be about part p etc
thanks
The garage will have three circuits. One lighting wired in 1mm twin an earth on a 6a type b circuit breaker. One power in 2.5/1.5mm twin an earth on a 20a type b circuit breaker. One circuit powering a 3kw water heater in 2.5/1.5mm on a 16a mcb.
I was goin to run 2 core, 10mm swa cable from the main consumer unit to the garage d.b. part clipped direct to the external house wall and part burried and use the swa as main earth. The d.b. will have fault protection by the 80a rcd in the house consumer unit. I will terminate the swa in two metal boxes attached flush with the c.u. and d.b. using usual banjo method.
I was going to use a 42a type b in the house comsumer unit feeding the swa. The house earth arrangement is tn-s and has a Ze of 0.12 and PFC of 2.2 Ka.
My main query is do i need an rcd in the garage d.b. (if so what size) and whether anyone would wire this job differently. I have done the calculations using design current etc and as far as i can tell it is all above board, but would appreciate someone else checking or giving useful feedback.
Also please dont feel the need to remind be about part p etc