Bright Sparks

I have just been on a site inspection which produced burnt out cables (Sheathing melted or burnt away), within some ground recessed fittings. I have not seen this used before and can only find reference to this cable (SY Cable) being used for Air-con, IT and food processing as a 'control' cable.

Having searched the web I find it is only suitable for use up to +70 Deg C, and within these fittings it will easily exceed that with a halogen lamp inside.

Would the choice of cable to be to blame? As un-suitable. What could I have suggested that should have been used? Rubber H0RN or SWA?

Thanks
 
The cable is tri-rated and the ends need crimping before termination and the appropriated gland needs using with this cable to give it IP protection from moisture getting into the braid, also the cable rating needs confirming for its use, halogen supply terminations are usually in a cooler part of the fittings but manufactureres instructions may need addressing, given all this i still think its been used and picked as a armoured cable which it isnt and wouldnt consider it for this use, the choice of cable would in my mind come down to the installation method you employ, example swa buried around perimeter up to joint boxes and flexed out to fitting as just one method available but ive little knowledge of your particular job at hand.
 
Ripped a load out last week all wired in SY they hadn't sealed them properly the water had worked it's way up the inner sheath via capillary action a good 4m along the wall it was clipped along. Wouldn't waste time with cheap ground lights they are a nightmare to seal LED all the way.
 

Reply to Use of SY 3 core in outdoor domestic lighting in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top