Bright Sparks
I have just been on a site inspection which produced burnt out cables (Sheathing melted or burnt away), within some ground recessed fittings. I have not seen this used before and can only find reference to this cable (SY Cable) being used for Air-con, IT and food processing as a 'control' cable.
Having searched the web I find it is only suitable for use up to +70 Deg C, and within these fittings it will easily exceed that with a halogen lamp inside.
Would the choice of cable to be to blame? As un-suitable. What could I have suggested that should have been used? Rubber H0RN or SWA?
Thanks