hoover

-
Joined
Jan 5, 2009
Messages
95
Reaction score
3
How accurate would the reading be? Want to do a quick test before the supply company comes to connect up. Don't have a proper earth rod tester but do have an Eli tester.
 
Haha, I normally use a 9v battery to do my pre dno connect up ze. After all a 9v battery and the supply are fed from same transformer. So it will give you a reading. Don't use a car battery that would just be silly, we all know they are not fed from same transformer!
 
How accurate would the reading be? Want to do a quick test before the supply company comes to connect up. Don't have a proper earth rod tester but do have an Eli tester.


Getting back to being serious, ....As this is a TT earthing system, which in all probability will have a high Ra value and that you don't have a dedicated earth tester, leave the testing until the DNO have made their connection. Then use your ELI tester to record the Ra value, ...if over the numbty 200 ohms Ra that BS7671 calls for, you will then have to add another rod onto the (hopefully installed) 5/8'' extendable rod. If you installed a thin 3/8'' non extendable twig, then you'll have to start all over again by installing 2 X 5/8'' coupled rods...
 

Reply to Using a generator to obtain a ze reading at earth rod. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

We’ve recently completed the first and second fix of a barn conversion that is off grid with solar PV, batteries and a back up generator. This...
Replies
0
Views
280
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top