Using a MCB as a main switch | on ElectriciansForums

Discuss Using a MCB as a main switch in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 9, 2016
Messages
235
Reaction score
103
Location
Liverpool
My boss has just took over a new site and I went to look the layout. Some boards are damaged some cables need replacing and am sure some other stuff. The site has a old busbar with isolators feed various boards and of her isolators. It also has a board connected directly on to the busbar . The main switch for this board is rated 125a the tails are 35mm ,but the fuse in the maintenance isolators are 250amp DD fuses. So the board and the tails have no protection. My question is (and I know it's late so be gentle) could I swap the main switch for a MCB , or will I have to relocate and feed it off a isolator with correct fuses (the board is a Hager tp and n Invicta3 ) . Now to go home and bed
 
Check out section 433 and 434 regarding placement of an OCPD at less than 3 meters Where there’s a change in the ccc of conductors and the following conditions it requires where overload and fault protection are placed on the load side.
 
Very common to have tails connected to a 250 amp busbar and then straight into an Isolator, I have seen 6mm2 tails connected to a 400 amp busbar before with the 32 amp Isolator bolted to it, very common practice years ago and you will see Busbars now still all over the country with the same set ups. In factories for example everything was bolted to a busbar and the tails from them to the busbar no where near the size of the incommer, no problem at all under this set up.
 
Very common to have tails connected to a 250 amp busbar and then straight into an Isolator, I have seen 6mm2 tails connected to a 400 amp busbar before with the 32 amp Isolator bolted to it, very common practice years ago and you will see Busbars now still all over the country with the same set ups. In factories for example everything was bolted to a busbar and the tails from them to the busbar no where near the size of the incommer, no problem at all under this set up.

It's still common practice among experienced electricians.

There are specific regs that allow this practice.
 
Unless I have read it incorrectly, the OP is saying the DB is fed direct from the busbar which feeds several circuits. So there is no overload protection for the tails feeding the DB.

There is also a 250A fused isolator in there somewhere but I can't decipher if it before the busbar chamber or betwixt chamber and DB.
 
I’m reading it, that there are 3 x 250A fuses, then the bus bar and then the feed to the DB taken off the bus bar.
Regulations allow protective devices to be installed within 3m of where a reduction in CCC of a conductor occurs.
If the 250A fuses are correct for the bus bar and the tails between the bus bar and the DB are less than 3m, there’s no problem.
 
Yes the 250ampnduses are protecting the whole busbar other isolators are connected going off the. Feed other stuff (not important) but the board in question is bolted on to the busbar with no peotprotec . I could of course remove the board and fit a isolator and relocate the board (but am lazy).tha t is why am asking about the MCB for main switch. (sorry if the details in my post was confusing , just wanted to give as much detail as Possible
 
I’m reading it, that there are 3 x 250A fuses, then the bus bar and then the feed to the DB taken off the bus bar.
Regulations allow protective devices to be installed within 3m of where a reduction in CCC of a conductor occurs.
If the 250A fuses are correct for the bus bar and the tails between the bus bar and the DB are less than 3m, there’s no problem.

There is a problem if the DB has the potential to take the current through those 35mm tails over what they can handle and lower than the 250A fuses.

Op - there needs to be some sort of OCPD between the bus bar and the DB. You need to ensure those tails can not be overloaded and if I have read the op correctly those tails, in there current state could be overloaded long before the 250A fuses blow.
 
Yes the 250ampnduses are protecting the whole busbar other isolators are connected going off the. Feed other stuff (not important) but the board in question is bolted on to the busbar with no peotprotec . I could of course remove the board and fit a isolator and relocate the board (but am lazy).tha t is why am asking about the MCB for main switch. (sorry if the details in my post was confusing , just wanted to give as much detail as Possible

Are you talking about replacing the main switch with say a 63A MCB in the DB?
 

Reply to Using a MCB as a main switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
816
I replaced a CU a few months ago along with isolator. Along comes Mr Eon meter man to fit a smart meter told the customer that he has to replace...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top