drzsta

-
Arms
Hi,

Scenario, Oil service to a church boiler is at the furthest point to the distribution board. Rather than run a separate bonding conductor to the oil service I've decided to bond the 3" cast iron heating pipework local to the DB then take a fly lead at the boiler from the CH pipework to the oil.

543.2.6 seems to permit this and I'm not worried about somebody adapting the pipework in future with plastic being that it's a church and the run is all on show.

Anybody have a different opinion on this?
 
Might be tricky to show that electrical continuity is assured,as per note (i),and you will need to show that it's cross sectional area is equivalent to the required size in copper.
 
Might be tricky to show that electrical continuity is assured,as per note (i),and you will need to show that it's cross sectional area is equivalent to the required size in copper.


Can't be much more "assured" than having heavy gauge screwed steel pipe. As for Csa equivalent pretty sure I'm good there too if 32mm conduit is equivalent to a 15mm2 copper cable.
 
Can't be much more "assured" than having heavy gauge screwed steel pipe. As for Csa equivalent pretty sure I'm good there too if 32mm conduit is equivalent to a 15mm2 copper cable.

I'm sure you are right, you could measure the resistance of the pipes and record it on the cert, and your call on whether 'pretty sure' is good enough regarding CSA equivalent.
 
Personally I would be happy with using continuous structural steel as a bridge over long distances but from experience service piping is prone to alteration or removal, as this would break the bond I wouldn't entertain the idea, because you are not using a continuous unbroken bonding wire that may do more than one service you do leave the possibility of the installation becoming unsafe due to other trades who lack understanding of bonding reqiurements.
 
Bit of a PITA to do it any other way. All of the run is exposed to the eye on natural stone walls. Micc would be the only decent looking alternative.

Interesting point, anything stopping me running a 2l2.5* micc as a bonding conductor and linking the inner cores and sheath together? Taking into account micc sheath Csa and conductor Csa I would be over the required main bonding size.

*because I have some in the garage
 
Bit of a PITA to do it any other way. All of the run is exposed to the eye on natural stone walls. Micc would be the only decent looking alternative.

Interesting point, anything stopping me running a 2l2.5* micc as a bonding conductor and linking the inner cores and sheath together? Taking into account micc sheath Csa and conductor Csa I would be over the required main bonding size.

*because I have some in the garage

If they can stand the cost of it then I see no problem with it, and I have given a bit of thought to this exact idea in the past when trying to overcome such a situation.
Although I'm sure it would confuse a few people looking at it I think you could reasonably sweat a lug directly on to the end of the MICC sheath.
 
If your calcs are done,and MICC would be aesthetically acceptable,why not use one of the cables or tapes used in lightning protection?

You could shine it up like MICC,it would be commensurately smaller,for the same CSA,and there are a good range of sturdy,tidy clips,applicable to that product.
 
If your calcs are done,and MICC would be aesthetically acceptable,why not use one of the cables or tapes used in lightning protection?

You could shine it up like MICC,it would be commensurately smaller,for the same CSA,and there are a good range of sturdy,tidy clips,applicable to that product.

That's a very good point, lightning conductor is available as a circular section solid bare copper conductor, although sizes probably start a bit bigger than 10mm!
 
There is two lightning conductor on our local clinic. one is the usual broad flat type , the other looked like 10 mm micro bore.
I believe it was stolen during the recent high copper prices.
 
At the risk of gilding a lily...the manufacturers of the standard sizes of lightning protection,also supply smaller sections and profiles.

These are commonly used for a vast array of tasks,including Cornish hipster jewelry!

I have used it for a myriad of projects,both electrical ,and not.

I thought of another use,only last night,whilst watching a 30 year old "Back to the Future"....now this proves my need to get out more...

Do you know the part,where he has to time hitting the copper wire stretched across the road,with both the lightning strike,and doing 88 mph?

...I thought his chances,would have been greatly enhanced,by having the conductor running in line with the road,which would increase the duration of contact,and ensure that strike impulse,made it to the Flux Capacitor....

I explained this practical tip,to my missus,as she watched the film....thus both spoiling the film,and making her wonder about her ongoing 26 year error :19:
 
If they can stand the cost of it then I see no problem with it, and I have given a bit of thought to this exact idea in the past when trying to overcome such a situation.
Although I'm sure it would confuse a few people looking at it I think you could reasonably sweat a lug directly on to the end of the MICC sheath.

Think I am going to give this a try, any preference to the lead ratio in the solder? unfortunately they don't teach sweated joints during your apprenticeship these days :sad_smile:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

drzsta

Arms
-
Joined
Location
out in the cold
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Using extraneous metal as bonding conductor
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
drzsta,
Last reply from
UKMeterman,
Replies
20
Views
3,660

Advert

Back
Top