atm84

-
Joined
Aug 7, 2011
Messages
834
Reaction score
94
I have recently come across a situation whereby instead of running a main equipotential bonding conductor from the MET to the incoming water someone had instead ran a short bond from the MET to some copper pipe in the mains cupboard and clamped it and then placed a bond on the pipe near the incoming water (at the other end of the property) and bonded to the incoming water there.

Wander lead method states 0.02 ohms resistance.

I know this is not good practice but where does it say in the regs it has to be a continuous conductor and that you can't do it.
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk


Yeah......look up the definition of a protective conductor!
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk

A main bond is a protective conductor.

You need to read exactly what is written in the regulations and not make assumptions.
The term protective conductor encompasses both cpc and all bonding conductors
 

Reply to Using pipe work to bond to incoming water in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
900
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top