I have recently come across a situation whereby instead of running a main equipotential bonding conductor from the MET to the incoming water someone had instead ran a short bond from the MET to some copper pipe in the mains cupboard and clamped it and then placed a bond on the pipe near the incoming water (at the other end of the property) and bonded to the incoming water there.

Wander lead method states 0.02 ohms resistance.

I know this is not good practice but where does it say in the regs it has to be a continuous conductor and that you can't do it.
 
regs. specify that the bond to an incoming service should be within 600mm of the point of entry to the building, or as close as practicable. the scenario you describe might be fine as it stands, but when wet-pants comes along and cuts out some copper andreplaces it with that crappy DIY plastic crap, then you've lost your bond to the extarneous incoming service.
 
Obviously not a good idea as Tel says.
GN8 says that if the bonding is looped between services (e.g. MET to gas then gas to water) the the conductor should remain unbroken.
However 543.2 says that a bonding conductor can be a variety of different materials (many of which would require numerous joints) but do specify that the continuity of the bonding should be assured.
 
This could also be one of the occasions,where a visual,physical examination,could provide a better indication of possible issues,as 1x PFC is not available on the MFT :cyclist:
 
Guys cheers for the comments. I agree not ideal but I explained the scenario about the plumber coming along and cutting the pipe and the connection being lost. The section in GN8 certainly does say about the connection being unbroken however this reads as more of a 'recommendation' than a 'requirement' and describes a slightly different scenario.

I would never do it myself, I think it's poor practice but at the moment there is a bond. The resistance meets regulations blah blah blah. Would anyone give it a code when carrying out EICR?
 
What kind of warnings are there about not removing the pipe work, or replacing it with plastic?
Anything on the EIC, or any labels affixed along the pipe work?
 
That's the bonding connection itself. Not the length of bonding cable. You can only work out what that should be by using the tables of resistance. Daz
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk


Yeah......look up the definition of a protective conductor!
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk

A main bond is a protective conductor.

You need to read exactly what is written in the regulations and not make assumptions.
The term protective conductor encompasses both cpc and all bonding conductors
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Using pipe work to bond to incoming water
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23
Unsolved
--

Advert

Thread statistics

Created
atm84,
Last reply from
davesparks,
Replies
23
Views
2,911

Advert

Back
Top