DilemmaFozz
Afternoon.
Ive just finished testing a very large industrial installation, made up of 5 units, and have come across various problems whilst there, and even more whilst filling in the form on the computer.
I am 2330, 2392, 2391 and 17th update qualified so yes I know what Im talking about and have done lots of testing and continue to do so but I havent tested anywhere this large (or old before)
Each unit contains AT LEAST 30 Distribution boards, plus various other things so I have tested over 150 boards and all necessary circuits (obviously only a sampling basis but it was more than enough!)
If anyone has any advice regarding these issues Id greatly appreciate the help;
1) 1 Unit has ALL of its distribution circuits protected by 3036 Re-wireables, I instantly failed pretty much the whole unit due to the fact the Pfc was 5.15 and obviously the 3036s can only take 4 and they all contain asbestos flash pads too. But am i right to do this? Ive pretty much told the customer he needs the factory rewired, the whole thing is in rewireables with various cotton cables and generally couldnt be arsed to go through all 20 odd 3036 consumer units noting everything and testing everything so i just noted down what I could (there was so little labelling and it was all so old and oily) and tested each boards Ze & Pfc to confirm if an earth was valid....which leads me on to
2) This entire unit has NO Earthing conductors between consumer units and no (at least I cant find any) bonding cables, is it acceptable for trunking to be used as an earth? I mean according to amtech a 100x100 metal trunking has a csa of 135mm which is obviously more than adequate but is the actual metalwork acceptable on its own? Id never dream of installing that if i was wiring the installation, I wouldnt rely on the trunking for anything other than holding my cable.
3) Has anyone used amtech and filled a BS form for the EICR?! The schedules are a F***ING NIGHTMARE! Why do I have to do such a massive load of tickboxes for each board, im going to be seeing those tickboxes in my sleep!!
4) Does heavy oil inside consumer units/lights/sockets etc count as anything negative on the EICR? I mean other than making my life vile and my clothes smell does it have any bad effect on the electrical installation itself? from what i can see everything is working well still enough (except the lowbays which have oil in due to the amount of light output being heavily decreased)
Thanks in advance, and if the remedial works come up and anyone in the Leicester area is after some work there may be some available
Ive just finished testing a very large industrial installation, made up of 5 units, and have come across various problems whilst there, and even more whilst filling in the form on the computer.
I am 2330, 2392, 2391 and 17th update qualified so yes I know what Im talking about and have done lots of testing and continue to do so but I havent tested anywhere this large (or old before)
Each unit contains AT LEAST 30 Distribution boards, plus various other things so I have tested over 150 boards and all necessary circuits (obviously only a sampling basis but it was more than enough!)
If anyone has any advice regarding these issues Id greatly appreciate the help;
1) 1 Unit has ALL of its distribution circuits protected by 3036 Re-wireables, I instantly failed pretty much the whole unit due to the fact the Pfc was 5.15 and obviously the 3036s can only take 4 and they all contain asbestos flash pads too. But am i right to do this? Ive pretty much told the customer he needs the factory rewired, the whole thing is in rewireables with various cotton cables and generally couldnt be arsed to go through all 20 odd 3036 consumer units noting everything and testing everything so i just noted down what I could (there was so little labelling and it was all so old and oily) and tested each boards Ze & Pfc to confirm if an earth was valid....which leads me on to
2) This entire unit has NO Earthing conductors between consumer units and no (at least I cant find any) bonding cables, is it acceptable for trunking to be used as an earth? I mean according to amtech a 100x100 metal trunking has a csa of 135mm which is obviously more than adequate but is the actual metalwork acceptable on its own? Id never dream of installing that if i was wiring the installation, I wouldnt rely on the trunking for anything other than holding my cable.
3) Has anyone used amtech and filled a BS form for the EICR?! The schedules are a F***ING NIGHTMARE! Why do I have to do such a massive load of tickboxes for each board, im going to be seeing those tickboxes in my sleep!!
4) Does heavy oil inside consumer units/lights/sockets etc count as anything negative on the EICR? I mean other than making my life vile and my clothes smell does it have any bad effect on the electrical installation itself? from what i can see everything is working well still enough (except the lowbays which have oil in due to the amount of light output being heavily decreased)
Thanks in advance, and if the remedial works come up and anyone in the Leicester area is after some work there may be some available