M

mspms

Good evening all. I wonder if anyone could give me a steer as to why I am getting very high Zs readings. I have been testin a circuit that has a R1+R2 of 0.23 ohms but I seem to be getting Zs reading on L-E of + 40ohms. L-N is coming in at 0.2ohms. The incoming fuse is a 63amp BS1361 an RCD main switch protecting all circuits. All other tests are fine. I am wondering whether it could be my meter not reading correctly on the Zs test. Any ideas?

Thanks all.
 
Change your plug tester unit!
But try a few contiuity tests through the unit first and see that there is not dirt in the connections or bent pins from dragging around in your tool bag.

Edit
No hang on 0.01ohms sounds a bit low for a standard value, could be, but 23kA is too high for a domestic CU.
 
Gentlemen, thankyou for your time and patience. I will try again with just my probes and see what I get. Just one other question; why does a main switch RCD trip whwn carrying out Zs testing? i had one the other day, another empty house and need to go back to sort it.
Kind regards.
 
I don't think some of my posts are being sent. I have tried my three probes at my socket terminals and am getting 0.01ohms with a PEFC of 24Ka. So I think the problem is solved.
Just one more thing; I had a RCD main swith ch trip on me whilst carrying out Zs test the other day. I need to go back and sort it ( It's an empty house) What could be causing the RCD main switch to trip? I was using my plug adapter again>
Many thanks.
 
I would still be worrying with those results.

0.01ohms for ZS??

24Ka ???

Wouldn't like to be in that house when that kind of fault current flows.

Your meter sounds f***ed - did they cock up the calibration?
 
something is definitely wrong here. to get a Zs of 0.01, you would have to have a -ve value for R1+R2 .l try and borrow another MFT.
 
I had a Fluke 1652 giving me readings like that once, sent it off to be calibrated all came back ok, but it still gave random readings, its now in the stores! Test at a socket then at the mcb for that circuit (not at main switch as the RCD needs to be taken into account). then at the main switch. Tell us what readings you get
 
Last edited by a moderator:
I don't think some of my posts are being sent. I have tried my three probes at my socket terminals and am getting 0.01ohms with a PEFC of 24Ka. So I think the problem is solved.
Just one more thing; I had a RCD main swith ch trip on me whilst carrying out Zs test the other day. I need to go back and sort it ( It's an empty house) What could be causing the RCD main switch to trip? I was using my plug adapter again>
Many thanks.

I would say that the problem here is far from solved. Firstly, I don't believe that figure for a second, so something wrong with either testing or meter. Secondly, do you know what a standard switch/MCB is rated at? Certainly not 24KA!!!
 

Reply to Very high Zs reading in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
429
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes, probably overthinkig, thanks.
Replies
6
Views
612
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top