Trainee
Evening all,
Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable coming in from the house and the SWA running to a single outdoor double socket down the garden, the IR test between L-E fails at 0.05 Mohms. When the ends of both cables are disconnected from each other, and the IR tests are done on each cable separately (L-N, L-E, N-E), everything passes! It's only when I test between the earth coming from the house and the line of the SWA that I get the 0.05Mohms. The SWA is being supplied by an FCU inside the house off of a kitchen ring. Supply is TN-C-S.
Any advise much appreciated!
Red
Went round to a clients house and did some tests on an outdoor socket. At the junction (in an IP rated wiska box) between the cable coming in from the house and the SWA running to a single outdoor double socket down the garden, the IR test between L-E fails at 0.05 Mohms. When the ends of both cables are disconnected from each other, and the IR tests are done on each cable separately (L-N, L-E, N-E), everything passes! It's only when I test between the earth coming from the house and the line of the SWA that I get the 0.05Mohms. The SWA is being supplied by an FCU inside the house off of a kitchen ring. Supply is TN-C-S.
Any advise much appreciated!
Red